190m run SWA underground, supplied from 3p+N 240mm sub main, each cabin total demand is 80A, worked out 35mm but volt drop is about 8%, would this be okay?
 
No 8% is not okay. Which cable is 190m long the 240.0 or the 35.0?
If the 35.0 what is the volt drop of the 240.0 because the drop is calculated from the source of supply assuming the 240.0 is from the source of supply.
 

Multicore 90°C Armoured Thermosetting Insulated Cables​

Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,

Voltage:400V

Load:44.34kW / 80A

Length:190m

Method of Installation direct in ground or in ducting in ground

Cable Size:35mm²
 

Multicore 90°C Armoured Thermosetting Insulated Cables​

Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,

Voltage:400V

Load:44.34kW / 80A

Length:190m

Method of Installation direct in ground or in ducting in ground

Cable Size:35mm²
For volt drop 35.0 in undersized.
 
That calculated from Cleveland cables.
@westward10 point is that is when you have a balanced 3-phase load so only the losses in L1-L3 are a factor as N current is near-zero, if you have just one cabin drawing 80A then you get double the drop (L & N losses) so I'm guessing that is the 8% mention above, but I have not actually checked it.

But as @James points out 80A seems a lot for a wooden cabin! If heater cooker, and shower all on at once maybe, but allowing a bit of diversity, and/or maybe a priority unit cooker/shower would drop the peak load and make the overall drop acceptable.
 
Going up from 35mm to meet drop is going to be expensive. However, it seems 80A draw for a log cabin is quite high, more than many flats have as a supply!

So before sizing the cable to meed VD for 80A on a single phase of the three, are you sure that it really is needing that much?

You don't need to meet VD at the supply OCPD current (though you can find issues with disconnection times if not careful there), nor even at the max permitted by the sum of load OCPDs, but you do need to meet it at all realistic levels of usage. Can you tell us the loads and assumptions you made for the 80A figure?
 

Reply to Log cabin supplies in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
704
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
604
  • Question
No, that is part of a different earthing system, don't mix the different earthing systems unless you have given proper engineering consideration...
2
Replies
27
Views
3K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top