Thanks folks I'm familiar with the formula, this is what I wasn't sure of
The socket circuit end to end test result
I associate end to end tests with Ring FCs :38:
I don't want to crash this, post with silly questions LOL
 
PM sent.

looking forward to your competition, just remember all the numbers = loki FIX lol


Loki

Haha, every comp i ever enter i always claim its a fix before the winner is even announced! I need to think of a decent question first off though.... hmmm
 
Thanks folks I'm familiar with the formula, this is what I wasn't sure of

I associate end to end tests with Ring FCs :38:
I don't want to crash this, post with silly questions LOL

**deleted**
Edited this post to stop myself looking a right tool cos I didn't read the fact it said radial in the original question, probably a good time to go bed now! [emoji1]
 
Last edited:
Thanks folks I'm familiar with the formula, this is what I wasn't sure of

I associate end to end tests with Ring FCs :38:
I don't want to crash this, post with silly questions LOL

No such thing as silly question in the TS.

an end to test can be done on either a radial circuit or RFC. I tried to save confusion by putting the word "radial" in the question twice.

Scenario, we have just installed new radial circuit in a house using 6242y flat T&E. A Radial Socket Circuit using 2.5mm with 1.5mm CPC/earth

The socket circuit end to end test result, R1 = 0.59

If this were a Ring Final Circuit, we would test end to end at the CU/DB and get a r1. If that result was 0.59 you would expect a reading of 0.98 for the r2. The r1+r2 would be:- 0.59 + 0.98 divided by 4 = 0.39

If the Ze reading was 0.17, you add these together to see what the expected Zs will be. r1+r2+Ze = 0.39+0.17= 0.56

Now that we know what it should be, we can test at each socket outlet and if the Zs readings are higher than 0.56, there must be something wrong! Terminations should be checked.
 
My book has just arrived with this mornings post, im blown away at what it contains to be honest, it will be a massive help when i go on to the inspection and testing in my Level 3 next year.

Thanks again Loki for a great gesture :icon4:
 
If this were a Ring Final Circuit, we would test end to end at the CU/DB and get a r1.
Thanks for the explanation Paul M - I have a fair handle the sums, used to calculate the theoretical yardsticks.
It's just how to physically measure the R1 on the radial that has me scratching my head. :book:
 
Thanks for the explanation Paul M - I have a fair handle the sums, used to calculate the theoretical yardsticks.
It's just how to physically measure the R1 on the radial that has me scratching my head. :book:

The only accurate way i can think of would be with a wander lead?
 
The only accurate way i can think of would be with a wander lead?
Thnks pennychew :thinking: That's what I was thinking, then I thought the cable wouldn't be the same CSA and would require more sums ??
 
You connect the wander lead up to your tester then null it so that wander lead is taken out of the equation... The other way would be to record the resistance of the wander lead first then subtract this from the overall measured resistance of the wander lead and the live conductor
 