So from the graph we can see that 1x5mm cable could take 42.5A. If 2x2.5mm in parallel can take more than that due to being able to dissipate heat more efficiently than 1x5mm then its CCC is more, so in answer to Murdochs question (regulation's aside as stated by Mr DS) it should be a C3 as its not dangerous??

Although its a ring with many points coming off of it (which could be very unbalanced) rather than just one end load (so not strickly speaking in parrallel as E54 showed), so perhaps it is a C2 as we cant assume the CCC>42.5A??

Glad we've cleared that up :smile5:

My rational is that the routing of the cable is unknown and that leaving the 40A RCBO in place "could" be dangerous and hence my view that the C2 was appropriate. My thinking was mainly on the fact that its the kitchen with the usual appliances connected including a hob and a cooker (both plugged in).

An interesting debate all the same
 
My rational is that the routing of the cable is unknown and that leaving the 40A RCBO in place "could" be dangerous and hence my view that the C2 was appropriate. My thinking was mainly on the fact that its the kitchen with the usual appliances connected including a hob and a cooker (both plugged in).

An interesting debate all the same

That argument is just as applicable to a 32A MCB
 

Reply to Lollipop circuit on a 40A RCBO in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
197
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
248
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
346

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top