tri cal elec

Bit of a first post but Ive encoutered some dangerous going on today at work. Im not the finished article and im not here for no, if you dont know what your doing you shouldnt be doing it malarky. If any one can tell me what the ---- is going on it would be most appreciated.

The job is a lights gone out with a big bang heard in a toilette. So me and my more knowledgeable! collegue attend the job.

What I found was a first.

Haveing flicked the breaker on it wasnt the lights that seemed to be the problem but only some sparks comeing out of a piece of conduit. There is a blanked of what I presume old light switch. After the mcb had been turned on after about 20 seconds you would start to here popping and crackling going on it the conduit, then after 40 seconds of this it would backfire sparks and a flash out of the bottom of it. Its been fine for ages at least 2 years. I notticed that someone has put up some surface mounted trunking on the wall and screwed it to the wall with raw plugs, the thing is they have only gone and done it slap bang onto of where the conduit is running under the plaster, honestly you could not have done it better if there was no paster. obviousy this is the problem or at least thats what im inclined to think. however as I say its been fine for at least 2 years no one in the team has never had a problem with it and the surface mounted trunking has not been recently put up certainly not in the year ive been there.

Any way if your still following and not enranged my thinking is this

For what ever reason the fact that someone has gone and drilled a piece of trunking to a wall falling slap bang in the middle of some metal conduit burrried in the wall which is carrying three lives to a old blanked of light switching point has now affected the instilation. some where along the circuit there is a live leakage. what i mean is that the nick in the cable or cables is causing the electricity to leak out of the conductor which is all the cracking which can be heard in the conduit and the bright spark whihc fires out of the end of it.

What would you hae done just so I can clock if they actually no what they are doing
 
im not here for no, if you dont know what your doing you shouldnt be doing it malarky.

Haveing flicked the breaker on it wasnt the lights that seemed to be the problem but only some sparks comeing out of a piece of conduit.
After the mcb had been turned on after about 20 seconds you would start to here popping and crackling going on it the conduit, then after 40 seconds of this it would backfire sparks and a flash out of the bottom of it.

The criticism you seek to avoid is frankly all you deserve.
 
Sounds like a live fault to the conduit which has poor continuity to earth which is restricting fault current and preventing the protective device tripping, got that.
 
The criticism you seek to avoid is frankly all you deserve.
i disagree some members seem to enjoy trolling op's who they feel know less than them . In some cases it fair to suggest to get a electrian in etc ,but alot of the time it just to belittle people . I enjoy the forum but was a bit weary posting the first time as i didn't want to get into daft arguments and come out feeling i know less than i did before post as i think it should be the other way around .
 
It seems to me this internet malarkey can be helpful and at times brutal for trainees
In the past the only one to knock some sense into you was the sparks who trained you,these days the knocking of sense can become a onslaught by the masses :)

Those who may have been upset can always take comfort
I have yet to meet anyone who knew what they were doing when they first set foot on the path to becoming a spark ;)
 

Reply to Looking for some wisdom not a kicking in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
Replies
8
Views
1K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
883

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top