Thanks Ian and Telectrix, yes my In is greater than my Ib and my Iz is greater than my In. If I used 4mm cable as mentioned before, my It would not be greater than my Iz using the 70 deg C tables, but i believe this (condition 3) unessary to meet once condition 1 & 2 are met. In saying that, I now plan to use a 6mm cable anyway therefore my It will be greater than my Iz. I see many people have mentioned about not protecting by an RCD, but I believed this was only the case where the RCD was nigated by a Risk assessment (411.3.3), personally I would prefer to fit one and would not nigated it. But would you be so kind as to maybe give reference to where the regs states this if other than by a Risk assessment? Many thanks, James?