Loop impedance measurement | on ElectriciansForums

Discuss Loop impedance measurement in the Electrical Engineering Chat area at ElectriciansForums.net

Joined
Oct 25, 2021
Messages
1
Reaction score
0
Location
Singapore
Hi, All

I have a megger LTW325 and fluke 1664FC to measure loop impedance by using high current mode. But both results are quite different. megger LTW325 is given a value 0.04ohms and fluke 1664fc is given a value 0.12 ohms. Means megger can give a current at 230V/0.04=5750A but fluke is only 230V/1.12=1916A.

Do you have any advices or expereince on this megger and fluke meter?
 
Something to discuss with the tech team of the manufacuturers as they would know details like that. They have been most helpful to me in the past when something of that nature has arisen.
 
Check you are using the probes supplied with the MFTs. The one I have (DiLOG) is "zeroed" at the factory for the supplied lead resistance and there is no provision for nulling that out (I asked them). It only takes 0.08 ohm to explain what you are seeing.

The other obvious things are clean connections on the probes and plugs, and if both meters are in-calibration (and have not be abused too much since they were checked).
 
Check you are using the probes supplied with the MFTs. The one I have (DiLOG) is "zeroed" at the factory for the supplied lead resistance and there is no provision for nulling that out (I asked them). It only takes 0.08 ohm to explain what you are seeing.

You sure about that? My 9110 uses one of the function keys for nulling - seems a bit odd that they'd make a meter on which replacement leads would cause errors. Conveniently, it holds that measurement until batteries are replaced.

Here's Rev2 manual for the 9118, which details lead zeroing around page 16.
 
Last edited by a moderator:
I think I found it did not change the Zs value and asked them, but I can check tomorrow by deliberately using higher R leads and nulling them for low-ohm measurement.
 
I believe that once leads are nulled, they're taken into account for any resistance measurement until batteries are replaced. Lead nulling process is separate from any test, but IIRC it has to be carried out on continuity setting.
 
Doesn't make any sense that they'd be factory nulled as this would be a nightmare if leads need to be replaced. Also makes little sense that the meter would hold details for leads, but only apply them to one particular test.
You are 100% right, but that implies a sensible design where the low-R null value is incorporated in to the Zs computation.

The jury is still out...
 
I couldn't find the leads, and discovered it won't null out the ~1.1 ohms of my 50m extension lead, but I did find that enabling/disabling the lead zero for low-ohms made no observable difference to the L-N PFC measured (was seeing about 0.21 - 0.22 ohms in all cases)
 

Reply to Loop impedance measurement in the Electrical Engineering Chat area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
693
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
342
I created a voltage drop spreadsheet for this sort of thing. I used to use it to calculate the drop when designing regular 230V lighting circuits...
Replies
24
Views
1K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top