try using 3 leads. i don't know the flukes, but with my megger 1553, using 2 leads on no trip will throw up "trip".
 
:welcome:Are connecting you MFT to the live at the switch, or the switched live with the switch in the OFF position? do you have continuity on the cpc?
 
:welcome:Are connecting you MFT to the live at the switch, or the switched live with the switch in the OFF position? do you have continuity on the cpc? ie is it connected to earth?
 
How about going to the fitting and performing a 3 lead test there? That would be a more accurate measure of the circuits Zs too. Although I am unsure whether you are actually testing the circuit for any reason, or is it just to get a feel for your meter?
 
yes,it is on,I am putting the earth lead on the cpc,and the live probe on the switch live,I will try it with all 3 probes,but I wouldn't be able to do that at a light switch would i? I would have to go to the rose,and on the video which is on you tube,by routledge textbooks they are doing it at the switch with 2 probes,which is the one i am trying to do,I am thinking the 1651 fluke isn't capable to test like that.
 
yes,it is on,I am putting the earth lead on the cpc,and the live probe on the switch live,I will try it with all 3 probes,but I wouldn't be able to do that at a light switch would i? I would have to go to the rose,and on the video which is on you tube,by routledge textbooks they are doing it at the switch with 2 probes,which is the one i am trying to do,I am thinking the 1651 fluke isn't capable to test like that.


I don't use a fluke but could possibly be that the tester requires you to use the 3 leads to confirm polarity.
 
Not used a fluke myself, but I think what a couple of people have suggested is to join the N-E probes before testing, rather than only using two, although this will depend on if the circuit is RCD protected.
 
yes,I am trying to get used to the meter,maybe I am watching too many videos on you tube with different meters and expecting mine to do the same,a lot of those look (are) a lot newer than mine
 

Reply to loop impedance on lighting circuit in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

  • Question
No live and neutral at the wall. But that would be the switch live right?
Replies
14
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top