loop impedance, temperature, cable factor.... | Page 2 | on ElectriciansForums

Discuss loop impedance, temperature, cable factor.... in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jun 13, 2017
Messages
87
Reaction score
47
Location
Peterborough
Hello
I'm not sure if this is the correct forum area to post this in, apologies if it isn't...

I've been working through some mock questions on-line, and found myself confused by this:

The measured value of loop impedance for a circuit is 0.83ohm.
If the temperature at the time of the test was 20C, and the cable is 70C (factor 1.2) what is the corrected value. Ze = 0.4ohm:
a) 0.43 ohm
b) 0.86 ohm
c) 0.996 ohm
d) 0.916 ohm

I just cant get my head around this!

Any help would be great!

Thanks in advance,

Gary
 
yeah, but the loop impedance of a circuit includes Ze.
The external impedance is not subject to the 1.2 correction factor
When calculating R1+R2 using 20 degrees tables during the design you apply the 1.2 correction factor to compensate for 70 degree operating temperature
External ze is not a factor during this
 
The generally accepted method of correcting for temperature is to apply it to the whole of the Zs for the circuit, however this does not , as said above provide an accurate assessment as the external supply may not be running at 70°C.
In that case the separation of Ze and R1+R2 may be undertaken and the correction factor applied to the R1+R2 only and the uncorrected Ze applied.
In the case of the question the method of calculation is not clarified.
Also the correction is from ambient (20°C) to 70°C rather than the usual correction of the tabulated value down to 20°C.
Basically you can apply the 1.2 correction factor to the 0.83Ω and get 0.996Ω
or you can apply the correction factor just to the back calculated R1+R2 (which should not be done) of 0.43Ω and add it to the Ze of 0.4Ω and get 0.916Ω.

Because the question specifies Ze you might assume they mean the more accurate correction but since it requires an unapproved calculation it seems odd.
 
The generally accepted method of correcting for temperature is to apply it to the whole of the Zs for the circuit, however this does not , as said above provide an accurate assessment as the external supply may not be running at 70°C.
In that case the separation of Ze and R1+R2 may be undertaken and the correction factor applied to the R1+R2 only and the uncorrected Ze applied.
In the case of the question the method of calculation is not clarified.
Also the correction is from ambient (20°C) to 70°C rather than the usual correction of the tabulated value down to 20°C.
Basically you can apply the 1.2 correction factor to the 0.83Ω and get 0.996Ω
or you can apply the correction factor just to the back calculated R1+R2 (which should not be done) of 0.43Ω and add it to the Ze of 0.4Ω and get 0.916Ω.

Because the question specifies Ze you might assume they mean the more accurate correction but since it requires an unapproved calculation it seems odd.
that was my interpretation. correction factors are usually applied to the Zs value in BS7671 , not jusrt to the R1+R2 values.

by calcularting i the way the question implies, it would be possible to get a borderline value above the recommended value to below it.
 
that was my interpretation. correction factors are usually applied to the Zs value in BS7671 , not jusrt to the R1+R2 values.
My first approach was to do just that as this is normally fine and is the first thing you would do and would only apply further accuracy if the value was out of range, but because they specify Ze, which is usually immaterial, I do wonder what they are going for.
Especially since they give both possible answers.:(
 
Yeah I thought because they have the Ze it was there for a reason. The question should have maybe stated that there were no possible parallel earth paths on the cct so you could accurately make an assumption as to the r1r2.

I forgot all about the tricky wording they use at C&G. Shame it's multiple choice, otherwise you could write both possible answers and the reasoning behind them.
 

Reply to loop impedance, temperature, cable factor.... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
776

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top