I was doing a Ze test today with my 1651 fluke and it was reading >2000 ohms.
The main switch was isolated and the earth disconnected. I had the green probe crocked onto the TN-S clamp on the incoming main, the blue on the neutral bar and the red on the supply side of the main switch.
Assuming there was a problem with the supply company's earthing I was about to call them when I thought I'll just do a Zs test on a socket outlet to be sure and I got a reading 0.8 ohms or something like that.
Would anyone mind telling me what is going on here? My tester just got back from being calibrated so I can only assume there is something I am doing wrong
I ended up calculating Ze from Zs-(R1+R2) as 0.1 ohm.
thank you for any ideas.
The main switch was isolated and the earth disconnected. I had the green probe crocked onto the TN-S clamp on the incoming main, the blue on the neutral bar and the red on the supply side of the main switch.
Assuming there was a problem with the supply company's earthing I was about to call them when I thought I'll just do a Zs test on a socket outlet to be sure and I got a reading 0.8 ohms or something like that.
Would anyone mind telling me what is going on here? My tester just got back from being calibrated so I can only assume there is something I am doing wrong
I ended up calculating Ze from Zs-(R1+R2) as 0.1 ohm.