I encountered a strange one the other day, new armoured supply to a shed, Ze at the Rcd main switch in the shed was 0.40, R1+R2 was 0.24 on the supply armour. When I did a earth loop on one if the sockets I got 1.09 which was high considering the run so I did a no trip test on the outgoing terminals of the Rcd incomer and got 0.96?. Swapped the Rcd and tried again, 0.90. I've just checked my tester at home and its working fine as I thought it could be the no trip function playing up. It was a BG board. Any explanations?? Could it be dodgy Rcd main switches? The second one was a new replacement from wholesalers.