Hi guys,
Today i went to a hotel that had lost its neutral at the main incommer, and has been presumed out for around a year. The neutral link had been undone during a previous refurb and tightened up in the undone position. The problem has only been found after a small fuse board from the blue phase caught fire. Most down light transformers/florries/coffee machines etc have been fried, though it has only really affected things on the blue phase.
My questions are how does everything keep working, as it has been for a year, without a neutral, im thinking either the neutral has only recently dropped out (but then why was it done up so tightly in the undone position) or the earth has been a return path for a year or so.
My other question is why is it that almost all of the equipment affected is fed from blue phase? Could it just be that blue phase just happens to have almost all of the electronic equipment on it.
I do not have a lot of details for the job, i expect i will be back there in a week or so, we only went down today for a few hours to rig up some tempoary lights to get them back up and running.
I do not know the earthing arrangement, and by all means correct me if my assumptions are wrong.
Here are a couple of photos of stuff i found whist investigating.
If the breaker doesnt fit? cut up the board.
Breaker doesnt fit? Bend the board
Some lovely melted cables
Getting a bit hot?
Oooh pretty colours
Cable doesnt fit? Give it a haircut.
Cheers,
Tim
Today i went to a hotel that had lost its neutral at the main incommer, and has been presumed out for around a year. The neutral link had been undone during a previous refurb and tightened up in the undone position. The problem has only been found after a small fuse board from the blue phase caught fire. Most down light transformers/florries/coffee machines etc have been fried, though it has only really affected things on the blue phase.
My questions are how does everything keep working, as it has been for a year, without a neutral, im thinking either the neutral has only recently dropped out (but then why was it done up so tightly in the undone position) or the earth has been a return path for a year or so.
My other question is why is it that almost all of the equipment affected is fed from blue phase? Could it just be that blue phase just happens to have almost all of the electronic equipment on it.
I do not have a lot of details for the job, i expect i will be back there in a week or so, we only went down today for a few hours to rig up some tempoary lights to get them back up and running.
I do not know the earthing arrangement, and by all means correct me if my assumptions are wrong.
Here are a couple of photos of stuff i found whist investigating.
If the breaker doesnt fit? cut up the board.
Breaker doesnt fit? Bend the board
Some lovely melted cables
Getting a bit hot?
Oooh pretty colours
Cable doesnt fit? Give it a haircut.
Cheers,
Tim