Hi guys,

Today i went to a hotel that had lost its neutral at the main incommer, and has been presumed out for around a year. The neutral link had been undone during a previous refurb and tightened up in the undone position. The problem has only been found after a small fuse board from the blue phase caught fire. Most down light transformers/florries/coffee machines etc have been fried, though it has only really affected things on the blue phase.

My questions are how does everything keep working, as it has been for a year, without a neutral, im thinking either the neutral has only recently dropped out (but then why was it done up so tightly in the undone position) or the earth has been a return path for a year or so.

My other question is why is it that almost all of the equipment affected is fed from blue phase? Could it just be that blue phase just happens to have almost all of the electronic equipment on it.

I do not have a lot of details for the job, i expect i will be back there in a week or so, we only went down today for a few hours to rig up some tempoary lights to get them back up and running.

I do not know the earthing arrangement, and by all means correct me if my assumptions are wrong.

Here are a couple of photos of stuff i found whist investigating.

If the breaker doesnt fit? cut up the board.
[ElectriciansForums.net] Lost neutral


Breaker doesnt fit? Bend the board
[ElectriciansForums.net] Lost neutral


Some lovely melted cables
[ElectriciansForums.net] Lost neutral


Getting a bit hot?
[ElectriciansForums.net] Lost neutral


Oooh pretty colours
[ElectriciansForums.net] Lost neutral


Cable doesnt fit? Give it a haircut.
[ElectriciansForums.net] Lost neutral


Cheers,
Tim
 
Im working for someone else atm and thats what ive advised, but i know they wont pay for it as the bodged refurb was only a year ago.

Ive counted over £1000 of led lamps blown already lol

To be honest, if they don't take you up on your offer of a rewire, then id probably be walking away.

You need to push for a rewire as strong and as hard as possible - it'll then teach people to get the job done correctly in the first place, and not always going for the cheapest option all the time. You any idea who's caused this carcrash? Like Archy said, get the client to give them a phonecall.
 
To be honest, if they don't take you up on your offer of a rewire, then id probably be walking away.

You need to push for a rewire as strong and as hard as possible - it'll then teach people to get the job done correctly in the first place, and not always going for the cheapest option all the time. You any idea who's caused this carcrash? Like Archy said, get the client to give them a phonecall.

I have told my boss that i wouldnt settle for less than a full rewire as we have no way of telling how many melted cables there are in ceiling void.

I know what company did the work, but i will refrain from mentioning them as its possible (but unlikly) that they were not the last to work on the buildings electrics. They are NIC members though.

Tim
 
if a spark insisted on a rewire of a commercial without at least providing a test & inspection report first they'd probably get laughed out of the building.

no ones gonna cough up the serious money needed for the work without proof - end of.
 
Biffs right, to add, suggesting a rewire to the customer without a report is not only laughable but could be embarrassing, I would have you removed from the building haha
 
To be honest, you're right on the EICR for the mess and use it as evidence.

But with the pictures the OP has provided the client can't be very bright if he can't see the danger for himself lol.

Aye, Mr.OP EICR it then label unsatisfactory...if it comes back satisfactory i will enter a civil partnership with MDJ :38:
 
Biffs right, to add, suggesting a rewire to the customer without a report is not only laughable but could be embarrassing, I would have you removed from the building haha

exactly.
even though it looks terrible , alot of the C2's could be fixed in a couple days so pulling a £5000 rewire quote out of your arse on the basis of some burn marks wont look too clever lol.
 
I understand where your coming from, my view was that given the amount of melted cables we found, i only took pictures of a couple of bits, testing may not show up the damage as the cables may not be touching anything else yet. There are cables with the insulation completly melted off for around a foot but the copper is not touching anything else.

I have only been to the job for half a day but there are guys from my firm still up there and they are backing what i have said as they have found more horrors in the ceiling, some is damage from the lost neutral and some is the botched refurb.

I will conceed that an eicr first would be the better route if nothing else but to provide proof of the faults that are possible to find through testing.

Thanks for the continued advice.

Tim
 

Reply to Lost neutral in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
333
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
859
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
985

Similar threads

  • Question
The loads in my instance were others circuits the loads being welders.
Replies
3
Views
926
S
  • Question
Yea its exactly that, its a photographed print out, the landlord is 85 😂 he is expecting 2 visits i was just trying to save myself the time, the...
Replies
4
Views
449
suffolkspark
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top