The tingle is when I'm standing on a tiled floor near the shower.

You haven't got underfloor electric heating by any chance have you?
Or was the bathroom floor covered in nailed down plywood before the tiles were put down?
 
Hi,

I have found out this since:
If the earth is disconnected from the shower unit the voltage on the shower hose goes up to 109V AC
When this happens the 3amp fuse in the switched spur doesn't blow and the RCD protecting the Ring main the spur is on doesn't trip either.

Needless to say I've turned it off at the double pole switch.

Is the shower knackered? Why didn't the fuse or RCD trip?

No underfloor heating, yes it is AC voltage, there are undoubtedly a few nails in the floor boards from when the house was built.
 
If the earth is disconnected from the shower unit the voltage on the shower hose goes up to 109V AC
When this happens the 3amp fuse in the switched spur doesn't blow and the RCD protecting the Ring main the spur is on doesn't trip either.Why didn't the fuse or RCD trip?
There's no reason for the fuse to blow or RCD to trip, there's voltage there, but no current flowing, apart from whatever is flowing through the meter.
 
You have created a potential divider , probably via capacitive coupling half way between N=0V AC
and Live =240 ..then lost a little due to the meter .
(not a very safe test) esp if nervous !
Leakage currents are just that , small currents doing no harm escaping to earth .
( Unless a fault occurs without Earth attached = danger)
 
Agree with above - but don't use the shower without earth connected as manufacturer intended :)
 
I have a hot/cold feed power shower in bathroom, shower frame and a radiator near by.
I'm measuring the voltage difference between the three things and getting the following and wondered if anyone could help. Had two sparky's out who have not thrown any light on it so far.
Shower hose (metal) to radiator 0.2v
Radiator to Shower frame 2v

When I run the shower for 2-5 mins I get these readings
Shower hose (metal) to radiator 5v
Radiator to Shower frame 12v

This voltage then very slowly drops back down to earlier figures over the course of mins/hours rather than seconds (in 5-10 mins it would drop from 12v to 10v)

I have this: Bonding from rad to both inlet pipes of shower
I was advised to do this which is now done: Bonding from earth in shower unit to the pipework feeds and supplementary bonding from pipework to two upstairs light rings which was advice sparky got from NIC

The shower is hot/cold so just a pump from a spur on ring main protected with switched fused 3a and RCCB on ring main circuit

If I switch off the bathroom lights the first 0.2v reading prior to running shower might drop from 0.2v to 0.1v

Nothing on the CU has tripped but there is a tiny spark when sparky took off an Earth from the (rail?) in the CU while he was looking at it.

No single circuit seems to be the cause of the low voltage readings but if everything is off on the CU the reading is 0v.

Any help ideas would be appreciated .
Cheers
Kris
I have a hot/cold feed power shower in bathroom, shower frame and a radiator near by.
I'm measuring the voltage difference between the three things and getting the following and wondered if anyone could help. Had two sparky's out who have not thrown any light on it so far.
Shower hose (metal) to radiator 0.2v
Radiator to Shower frame 2v

When I run the shower for 2-5 mins I get these readings
Shower hose (metal) to radiator 5v
Radiator to Shower frame 12v

This voltage then very slowly drops back down to earlier figures over the course of mins/hours rather than seconds (in 5-10 mins it would drop from 12v to 10v)

I have this: Bonding from rad to both inlet pipes of shower
I was advised to do this which is now done: Bonding from earth in shower unit to the pipework feeds and supplementary bonding from pipework to two upstairs light rings which was advice sparky got from NIC

The shower is hot/cold so just a pump from a spur on ring main protected with switched fused 3a and RCCB on ring main circuit

If I switch off the bathroom lights the first 0.2v reading prior to running shower might drop from 0.2v to 0.1v

Nothing on the CU has tripped but there is a tiny spark when sparky took off an Earth from the (rail?) in the CU while he was looking at it.

No single circuit seems to be the cause of the low voltage readings but if everything is off on the CU the reading is 0v.

Any help ideas would be appreciated .
Cheers
Kris
 
This reminds me of when years ago house bashing house been fully tasted ,RCD to sockets only split board supplementary bonding between hot cold ,rad and upstairs lighting circuit. The homeowner complained regarding getting tingle between rad and shower (not electric).Measured it and was 12v did insulation resistance test and found low reading on downstairs lights located it to outside lighting cable that where installed outside light taken down ,cable end cut and tapped up that when rained dampness between live and earth not enough to trip mcb.
 
Don't just lurk around in the background bak1950, post some replies or start some threads, after all its been over 7 years. By the way sparksburntout is the head teacher on spelling mistakes or bad grammar. :)
 

Reply to Low Earth Voltage in bathroom from bonded fittings in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

  • Question
The chances of any problem without the RCD are minimal, including it extremely negligible......with the supplementary, on a kin to Hannibal Lector...
Replies
6
Views
670
T
  • Article
New plumbing & heating system advice Hello, I'm installing a new central heating & plumbing system and just wanted to run through my design...
Replies
0
Views
186
Tommyh311
T
T
  • Article
New plumbing & heating system advice Hello, I'm installing a new central heating & plumbing system and just wanted to run through my design...
Replies
0
Views
196
tommyh311
T
Question 1 do you prefer buttered, salted or sweet salted? I'm guessing salty 😜 1. Auto range multimeter (used on mains before when testing the...
Replies
2
Views
480
  • Question
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
796

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks