also test N/E with and without main bonding connected. surprising what plumbers can do when you let em loose with a blowlamp close to cables.
do you have RCD's on the circuit?
try disconnecting your earth and neutral in the board to make sure you are not picking up a N-E fault on another circuit eg the immersion. also a continuity check between your disconnected E and the rest of the E's and yout N and the rest of the N's will confirm no supp bonding issues or borrowed N issues (with main switch off mind).
Reply to Low insulation resistance reading neutral to earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...