Justintime
Hello All wondering if anyone could shed some light on a problem i have with my IR readings.
I recently rewired a house.. took care pulling cables in etc . finished 1st fix, checked cables by looping ring main in connector blocks and doing continuity and IR test . continuity was ok, IR read >999. everything fine.
Few weeks later came back..
2nd fixed , mounted board , terminated , sockets on tested circuits , all tests were fine apart from my IR readings on the ring mains>?? readings between N/E conductors was around the 1.6Mohms. and L/N around 2.3mohms
Investigated, Disconnected main earth & neutral . split the ring in half, took socket off to see which side the problem was on and both halves were reading >999 on both legs & all conductors?? i thought that socket was the problem so i tested by replacing with connector blocks but once loop was complete the readings dropped right down again??
the sockets are hager.. so not too cheap i cant understand why this is happening, can anyone help
I recently rewired a house.. took care pulling cables in etc . finished 1st fix, checked cables by looping ring main in connector blocks and doing continuity and IR test . continuity was ok, IR read >999. everything fine.
Few weeks later came back..
2nd fixed , mounted board , terminated , sockets on tested circuits , all tests were fine apart from my IR readings on the ring mains>?? readings between N/E conductors was around the 1.6Mohms. and L/N around 2.3mohms
Investigated, Disconnected main earth & neutral . split the ring in half, took socket off to see which side the problem was on and both halves were reading >999 on both legs & all conductors?? i thought that socket was the problem so i tested by replacing with connector blocks but once loop was complete the readings dropped right down again??
the sockets are hager.. so not too cheap i cant understand why this is happening, can anyone help