Hello All wondering if anyone could shed some light on a problem i have with my IR readings.

I recently rewired a house.. took care pulling cables in etc . finished 1st fix, checked cables by looping ring main in connector blocks and doing continuity and IR test . continuity was ok, IR read >999. everything fine.

Few weeks later came back..

2nd fixed , mounted board , terminated , sockets on tested circuits , all tests were fine apart from my IR readings on the ring mains>?? readings between N/E conductors was around the 1.6Mohms. and L/N around 2.3mohms

Investigated, Disconnected main earth & neutral . split the ring in half, took socket off to see which side the problem was on and both halves were reading >999 on both legs & all conductors?? i thought that socket was the problem so i tested by replacing with connector blocks but once loop was complete the readings dropped right down again??

the sockets are hager.. so not too cheap i cant understand why this is happening, can anyone help
 
Have you tested the sockets themselves? Has it been recently plastered? If all the conductors are testing out ok then its a good bet that the sockets themselves are damp. I'd test them to see and if the IR is low then as you said let them dry out and test again. This way you can rule out a faulty batch of sockets, which is unlikely but possible.

Yes was recently platered around a month ago tho, I've meggered sockets That's fine Knowing the circuit is compliment in connector blocks is good enough for me. They can crack on getting the floor down

Thanks
 

Reply to Low Insulation resistance readings when connecting final socket on ring? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
400
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
356
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top