As said, it is probably a load you haven't disconnected but it does no harm chasing it down just in case.

Just a hint though, if it is low at 250V it really isn't a good idea to test at 500V or when you do find that load you missed you might just find yourself replacing it free of charge after it has objected to 500V up its chuff.... :(
 
Cheers Guys,

Yes, when I read similar threads they said the same. Why does it make it ok if you have a good Live/neutral combined IR reading? The IR between L and N is still poor and could mean a problem? (Although I'm guessing it doesn't as otherwise you guys wouldn't have said it!). Why does the good reading between L+N combined and E show that it is an appliance still not accounted for and not a wiring/damp/poor insulation problem?

If the low reading was caused by damp, I would expect to find L-E/N-E readings to be of very similar values as the L-N readings as I'd expect damp to affect all conductors.
I'd say, by your readings that you have load connected somewhere, reconnect the circuit, power up and put clamp meter on it, to see if there is any load being drawn, this may help you identify what's on there.
 
I have had this similar reading before a few times funnily enough. I am pretty sure it is the RCD coil. Make sure the rcd is not included in any part of the test
 
I have low readings such like before, it's just tracking down the load. What about pir light connected straight onto the supply (i.e. no switch). Favourite is socket wired into the lighting for loft tv booster, or even a shower pump!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Low IR readings on lighting circuit - 0.654 Mohms
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
Midwest,
Replies
22
Views
7,545

Advert

TrueNAS JBOD Storage Server

Back
Top