Hi,guys went to do an EICR and when doing IR test I got L-E ON RFC like 0.02 MOHM and two lighting circuits L-E AND L-N the results were like 0,14 and 0,15 MOHM.It is old wiring where all the cables live and neutrals are black put in the walls in steel conduit.My question is is it possible that low readings are due to dumpness in the wall?Took one light down and can see dumpness on the cables.Doe to time limit coulf not disconnect everything,but surely L-E and N-E should give some higher readings.Thank uou in advance for all help.
 
Check if there are any RCD sockets/FCU on the circuit.

I have been caught before discovering they have a low-ish internal resistance to the CPC (presumably to trip if wiring fault?) and after disconnecting them it went to the ~10M or so I would prefer to see.
 
Filtered sockets or extension blocks always cause low IR readings on RFC's
This is another good point. If you ever see low IR then re-test at 250V, if you get a really big difference (going from < 1M to > 10M sort of thing) then it has all the hallmarks of an SPD in some multi-way block or similar.
 

Reply to Low IR test readings on lighting and RFC. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

Induced voltage can be a bit of a red herring when using DVM my guess is somethings moist.
Replies
5
Views
426
T
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top