Here's an interesting one... :)

Amongst other things, was asked to replace a 1G exterior socket with a 2G. Did some basic checks before I started, including IR (L+N to E) on the RCBO-protected socket RFC. ~0.26MΩ, uh oh. Sigh theatrically, ponders a day of unplugging everything then splitting down the ring etc.

However, given that the exterior socket was supplying a small pond fountain, I thought I'd try that first. Unplug it, and low and behold the IR reading goes up to a more healthy 27.4MΩ.

What initially struck me as odd was that the existing 1G socket was wired like this:

[ElectriciansForums.net] Low IR to earth (with no CPC)

:eek:

So I tried a little experiment:

[ElectriciansForums.net] Low IR to earth (with no CPC)


(test was done at 250V, tester says 0V as test had completed).

Logically, it all checks out... but it still amused me that I could just lightly poke my test probe into the gravel and it give pretty much the same reading I was getting in the house. :)
 
What initially struck me as odd was that the existing 1G socket was wired like this

Mmmm..bet they disconnected that cpc to increase the earth fault impedance and reduce the leakage on that failing pump to get a bit more life out the old girl haha. That RCBO wouldn't stay in at 0.26 with cpc connected. Devils ain't they lol
 
Mmmm..bet they disconnected that cpc to increase the earth fault impedance and reduce the leakage on that failing pump to get a bit more life out the old girl haha. That RCBO wouldn't stay in at 0.26 with cpc connected. Devils ain't they lol

The RCBO shouldn't trip with an L-E IR of 0.26M ohm... that's a leakage current of 0.9mA.
 
Against my advice, the client has continued to use the old fountain pump, and no it doesn't trip the RCBO. They promised they'll look into getting a new one.

I see what you mean about the aesthetics of the KT63, it is a bit random! :) But I do like my little Kewtech - you can tell what every button does, you don't have to remember things like, "F3 for null" or "<--> for a different setting."
 
Yep, indeed, I stand corrected. About 0.10M ohm is more like it going that the 30ma's trip on ramp at around 22ma I find.

Still a ropey old pump though and well ready for the bin!
Wouldn't that be a trip at around 0.01MΩ at 22mA, not 0.1MΩ?
 
Against my advice, the client has continued to use the old fountain pump, and no it doesn't trip the RCBO. They promised they'll look into getting a new one.

I see what you mean about the aesthetics of the KT63, it is a bit random! :) But I do like my little Kewtech - you can tell what every button does, you don't have to remember things like, "F3 for null" or "<--> for a different setting."
Hi Steve.

I've sometimes got poor IR results and then when everything is unplugged they disappear. In otherwords it's the appliance that is 'possibly' faulty.

I remember DaveSparks reminding me once that when we IR test we are just testing the fixed wiring. I personally don't have enough knowledge of each appliance to know whether it should have any kind of pathway to earth and if a measurement of <1MΩ signifies a faulty appliance. Would a PAT test not be required in this case before recommending an appliance not be used. (Saying that, I do remember back when I started I traced poor IR results to an extension lead and suggested it was faulty, all it was was surge protection! :rolleyes:). I also remember lucien explaining that it is rare for an appliance to have an intended 'lower' IR reading to earth but not impossible.

I''d be putting the CPC back into the socket rather than the box and putting the reading as 27.4MΩ as that is the correct reading for the fixed wiring. I would still advise the customer to get the pump looked at but I'd make it clear that I can't say for sure if it is faulty.

Of course, saying all that, you have a better understanding of these things than I do, plus you've worked with boats where I guess you dealt with pumps.... so perhaps you can say it's faulty. I shall await to be put in my place :)
 
I replaced the cover on my brothers outdoor socket. CPC terminated into the back box as well. Wonder if it was the same sparks :)
That weren't no spark. From the client's recollection, it was "the blokes that put up the conservatory." Kinda figures...

Why provide the earth terminal at all? I can see the point on a surface mount pattress (if used for single pole switches) but putting one on a socket enclosure, I just feel like the manufacturers are trolling us. "We'll just put this here, see if anyone falls for the bait..." :)
 

Reply to Low IR to earth (with no CPC) in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
244
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
257
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
348

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top