sima24

Hi guys can anyone give any ideas on these low readings i have. On both rings im getting 0.7 / 0.8 ohms across everything, triple checked everything is unplugged, a pretty new installation, all other tests fine, im ripping my hair out
 
Split the ring in half and test as 2 radials, this will tell you where the fault is, you can then break it down further to find the exact point
 
And your getting the same low reading on both RFC's? I reckon it's time to split the rings. I had one the other day where I ended up testing between each socket to eventually find a cable that had been pulled through a joist so badly the insulation had been dragged off. Admittedly this wasn't on both circuits!!

Split one ring mid point ish and IR test it again.

Just another point, are you sure you have got the right ends for both rings??
 
Do you have the MS and RCD's turned off, and if it is RCBO's have you disconnected the fly leads to perform the dead tests?
 
Cheers,
My readings so far
Upstairs ring
L-N 0.8
L-E 2.8
N-E 2.7

Downstairs ring
L-N 0.00
L-E 1.05
N-E 1.06

you need to change the range to get an accurate reading for downstairs L-N, but it looks like a load is still connected to the circuit
 
if its on both rings and the rings are def correct first thing i would do is disconnect from DB all together, and split each ring, only work on one at a time, part of the ring must be clear, work back from the centre, if its not the plaster, not the RCBO / RCD and its still showing fault, remove 2 socket faces, test the link in-between, and repeat for next link, etc etc
 
Thanks, no wet plaster, house was built about 7-10 years ago. Things im thinking are neon switched spurs, bell transformer etc.
 
Hi. I realise on your opening list you said you did this but.... Worth checking again. All double pole fcu off and everything unplugged? What about the non switched fcu's they are single pole so remove fuse and link out the neutrals. Tv amp in loft off of rfc ?
 
Outside lights, spur to garage, the list goes on. But with those readings I'd put money on things still being connected to the circuits
 

Reply to low ir in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top