Hi all,
Just installed a brand new radial circuit for the upstairs sockets with Prysmian 2.5mm T+E, around 21 metres in length. When testing the insulation resistance of the circuit upon connection to the consumer unit, I seem to repeatedly get around 49 Megohms when measuring Neutral to Earth. The result seems to get lower as I lower the test voltage, and is more around 100 Megohms when testing at 1000v. I thought that it may be a dodgy bit of cable so separated the conductors at a few sockets and tested again but get the same results each time, sometimes as low as 26 Megohms. Line to earth and line to neutral are both at least 400 Megohms at each location. I tested the remainder of the 100M drum which probably still has around 80M left on it at 1000V, and get >1000 Megohms between conductors. 49 Megohms doesn't quite satisfy me for a brand new circuit. Any thoughts?
 
Hi all,
Just installed a brand new radial circuit for the upstairs sockets with Prysmian 2.5mm T+E, around 21 metres in length. When testing the insulation resistance of the circuit upon connection to the consumer unit, I seem to repeatedly get around 49 Megohms when measuring Neutral to Earth. The result seems to get lower as I lower the test voltage, and is more around 100 Megohms when testing at 1000v. I thought that it may be a dodgy bit of cable so separated the conductors at a few sockets and tested again but get the same results each time, sometimes as low as 26 Megohms. Line to earth and line to neutral are both at least 400 Megohms at each location. I tested the remainder of the 100M drum which probably still has around 80M left on it at 1000V, and get >1000 Megohms between conductors. 49 Megohms doesn't quite satisfy me for a brand new circuit. Any thoughts?
What MFT are you using?
 
As Derek mentioned, have you tested this whilst the circuit is connected at the consumer board, if so that might be the problem. Test again with the circuit completely isolate from the CCU.
But as westward stated 26 meg is not low.
 
The fact that the bulk cable reads good and the resistance increases with voltage both point to condensation in the socket outlets, especially if they are in rooms that are not continuously heated or there is plaster drying nearby. Opening them to split the circuit may be lowering the readings as more condensation takes place around the terminals. You might be able to prove it if you can find a section with a lowish reading and warm the associated sockets front and back with a fanheater for a few minutes.
 
Yes I tested the cable before it was even connected to the terminals in the CU. I have just retested the circuit again and have now got 67 meg. Using a Fluke 1662 MFT. Not too worried just originally 26 didn't quite satisfy me as high enough for a brand new circuit. Thanks.
 

Reply to Low N/E insulation resistance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
Replies
24
Views
3K
If I understand you right, every circuit individually achieves over 200MΩ but when the neutrals are commoned, one circuit reads 1.4kΩ L-E? Do we...
Replies
4
Views
2K
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
Replies
20
Views
1K
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
378
  • Question
Big tv and gaming pc for sale. Both work, honest. 😉
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks