Bazultra

I am currently testing a ring circuit with an r1 of 1.12 an rn of 1.12 and an r2 of 1.80
I have carried out my figure 8 test only to find that i have varying readings at the sockets between 0.40 and 0.80. How is it that I could be getting a low reading such as 0.40 with no parallel paths. I have made double sure I have carried out the figure 8 test correctly. Could this indicate a ring in a ring?
 
from you r1 and r2 readings, you would expect R1+R2 at each outlet to be about 0.75ohms.
 
Have you tried retesting the end to end values and making sure you have a good connection to the cable ends, a variation of 0.16 / 0.32 Ω could by caused by contact resistance or loose lead connections.
I assume the values you are measuring are for the r1 / rn figure 8?
Alternatively you could still have the ends the wrong way round and it is just a long run to the first socket.
What results do you get if you swap the connections round the other way?
 
deleted due to incriminating myself for being stupid.
 
Last edited:
You can get a low reading when doing a fig 8 test if you have a boiler circuit that has crossbonding, even with the load disconnected leaving the earths connected will give a lower reading as you aproch the spur. Look for something like that. Even a forgotton washing machine plunged in will cause this.
 
You can get a low reading when doing a fig 8 test if you have a boiler circuit that has crossbonding, even with the load disconnected leaving the earths connected will give a lower reading as you aproch the spur. Look for something like that. Even a forgotton washing machine plunged in will cause this.
It is surprising how many "testers" forget that disconnecting items from a RFC,may include what you have discussed,and leaving conductors,other than the line,still connected,can affect results. If only every RFC was as drawn in a text book...just posted about one i went to, a mixture of upstairs and downstairs radials,joined at one MCB,with at least two interconnections,and spurs going everywhere...extractors,boosters,garden lighting and a whole recently fitted kitchen...marvelous :pirate:
 

Reply to Low R1+R2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
429
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Also,if you had a duel box with a lighting cct on one side you would get a false reading.
Replies
2
Views
507
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top