So Ze=0.02 and R1+R2 = 0.73 on a first floor ring main.
Nearest submain is about 35m away, so that Ze's plausible, and even a slightly indirect route makes Ze=0.03 realistic. So MCBs are going to need changing to Type Cs.
Unfortunately for that first floor ring R1+R2 of 0.73 is too high for a 32A Type C. Yes I've got behind every point on the circuit, empty house so nothing hidden, no poor connections there, perhaps a JB hidden away under the floor somewhere but I'm not about to tear apart a (very nicely done up) house on a maybe when there's simpler things to do.
My first thought is "aha, but it is low enough for a 20A Type C!" which is how I intend to go about it right now, should still be enough power I think.
The idea I've just had though, and forgive me if this is dumb, it's late alright? is to split the circuit into two radials, so that one side goes to the large room at the front and the other goes to the two bedrooms, and put them on 16A breakers, allowing for more current overall if slightly less max load in each area.
TLDR: Low Ze, needs changing from Type B to Type C breakers. Either cut 32A ring with R1+R2=0.73 down to 20A or make into two 16A radials?
Thoughts?
Nearest submain is about 35m away, so that Ze's plausible, and even a slightly indirect route makes Ze=0.03 realistic. So MCBs are going to need changing to Type Cs.
Unfortunately for that first floor ring R1+R2 of 0.73 is too high for a 32A Type C. Yes I've got behind every point on the circuit, empty house so nothing hidden, no poor connections there, perhaps a JB hidden away under the floor somewhere but I'm not about to tear apart a (very nicely done up) house on a maybe when there's simpler things to do.
My first thought is "aha, but it is low enough for a 20A Type C!" which is how I intend to go about it right now, should still be enough power I think.
The idea I've just had though, and forgive me if this is dumb, it's late alright? is to split the circuit into two radials, so that one side goes to the large room at the front and the other goes to the two bedrooms, and put them on 16A breakers, allowing for more current overall if slightly less max load in each area.
TLDR: Low Ze, needs changing from Type B to Type C breakers. Either cut 32A ring with R1+R2=0.73 down to 20A or make into two 16A radials?
Thoughts?