Hi guys, I've got a TT system with a Ze of 21 ohms. Two ring final circuits are on the same rcd and are both giving a Zs of 1.7 ohms - does this indicate a neutral - earth fault?
 
Hello

It might be indicating that your parallel path back through a water Main Equipotential Bond or Gas is connected to another property with TNCS, bringing your reading down massively. From that figure I am a betting man on it.

Do you catch my drift, so to speak?

Could be gas or oil also. Or something else!

SPARTYKUS.
 
Thanks for the answers. There's no bonding to this board - it's a sub db in a garage fed from a 100 amp isolator. Anything else it could be? I haven't had time to do
many tests but would like a heads up before I go back tomorrow!
 
One core of swa is connected to MET, the other end connected to earth bar in db. No bonding in db. I have 3 rfc, 2 lighting circuits, 1 circuit to an outbuilding and 1 circuit feeding central heating. The garage is attached to the house and has living space above. The water is bonded to the main db in the house.
 
there maybe no bonding but if there is a boiler and the cable supplying the boiler has a cpc then that will make contact with the pipe work.

here is an idea why not do some dead testing, it's dead easy and a dead cert on finding a problem, dead. (got one more in)
 
The problem is that even if there is a parallel path through the water system the whole property is on tt and there's only one neighbour within a mile so I can't see it being a shared tn
 
that has nothing to do with it, any earthing system will have a parallel paths to earth. Just do a dead test, cos i bet ya aint done that yet!
 
The house has 2 boards and another in the garage. All are tt. I'll do the whole range of tests tomorrow and post the results!
 
Last edited by a moderator:

Reply to Low ZS on a TT system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
701

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top