Found a mains voltage fan on the wall inside a shower enclosure today,just next to the shower head.So am proposing to change to LV Fan and transformer outside,assume fan will need to be IP x4 or above even though LV.Thanks in advance.
 
is the fan on rcd ?
what IP rateing is the fan ?
i think u can get away with it if IP rating is x4 but it was a long time ago i spoke to niceic about it i saved it and here it it
Thank you for your enquiry to which I refer.

230V Ventilation equipment rated to at least IPX4 can go in Zone 1 with a shower. If there are water jets, e.g. for cleaning purposes, the equipment will need to IPX5 rated.

I have attached NICEIC Pocket Guide 1 for your information.

Regards,

NICEIC Technical.
 
Last edited by a moderator:
As long as the equipment is suitably rated for the zone, there are no prohibitions in BS7671 on using LV equipment in Zone 1.
Otherwise we would not be allowed LV showers.
 
Thanks for reply's.Its all on rcd but not happy with existing mains voltage fan.No access into ceiling above so fan is through the wall just next to the spray head which is flexible,so definitely spray jets.
 

Reply to LV Fan in Zone 1 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Question
Many thanks all for the advise and suggestions. I’ll give the client the option of extractor fans
Replies
8
Views
2K
You can replace a fan in zone 1 with a 230 volt fan with a pull cord, with an IP rating of at least IPX5, as long as the circuit is protected by a...
Replies
1
Views
1K
loz2754
L
  • Question
ok cheers for the help lads
Replies
7
Views
574
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
378
Sorry, 3. Should read: separate circuit from consumer unit with 16amp radial supply only to this lighting/camera…
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks