to achieve this it is recomended that the resitance of the conductor does not exceed 0.05ohms

apart from that the formula relates to the sizing of supplementary bonding conductors where disconnections times can not be met we are not talking about supp bonds but main bonds which is to ensure no difference in potential will occur between parts.

Lol, I suppose we are not talking about cross bonding then? Where did the disconnection times not being met come from?
I thought we are discussing the effectiveness of supplementary (cross) bonding to clamp the voltage below the maximum touch voltage even when disconnection times are met and where a fault might occur.

However, It is unlikely that cross bonding would be required for normal locations that are not within a bathroom. As long as the main protective bonding is in place and the disconnection times were met which is likely to be a lot less than 0.4s (0.01s).
The rule of thumb for the main protective bonding is as you say is 0.05 Ohms....
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Main Bonding and Cross Bonding question?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
43

Advert

Thread statistics

Created
chrisgc,
Last reply from
palmerelectrcal,
Replies
43
Views
7,966

Advert

Back
Top