Looking at pic that is a LPG bulk tank supply or a gas supply from a exsternal gas meter. I don't think you will find a meter in that house.
 
Looking at pic that is a LPG bulk tank supply or a gas supply from a exsternal gas meter. I don't think you will find a meter in that house.


Get the trumpets out - you are indeed right - the gas tank is around an outbuilding - I looked this morning.

So where does the gas main bond go then??
 
1/ It appears that you have a 16mm2 earthing conductor from the electrode
2/ Main protective bonding should be applied to all metal services entering the property although it might be argued from the pictures that the gas pipe may not be extraneous.
3/ A long lead test to ensure there is sufficient continuity between all the metalwork
BTW the 415.2.2 does not necessarily mean a value of 0.05 Ohms must be achieved since it relates to Ia or the possible fault current that might flow from the largest appliance/circuit in the vicinity of the pipework.

R=50/Ia. If the only electrical circuit is supplying a 3kW heater element then the Ia will be, worst case, 5 times the rating of the MCB. In this case is likely to be 16A times 5 = 80A ( most likely 50A) which will require an overall resistance of between 4.6 - 2.8 Ohms. However, if the simultaneously accessible metalwork is next to a 10.5kW instantaneous water heater then the likely fault current will be in the order of 0.9 Ohms. These are the worst cases which is why a 0.05 Ohms value is used to ensure that there is a minimum measurable resistance value between pipework .

I hope that provides sufficient smoke to clear the issue:dizzy2::cheesy:
 
cross bonding was and is part of the gas regs (but for some obscure reason they seem to think its our responsability)

0.05 ohms reading on main bonds is the same rule as supp bonds, it ensures that under single fault conditions a potential difference of -+ 50v (safe touch) does not appear on the pipework, by limiting the resistance (for 10mm) to 0.05ohms upto 27metres(or there abouts)

alternatively you could calculate the actual size using Rcalc allready provided.
 
Last edited by a moderator:
R=50/Ia. If the only electrical circuit is supplying a 3kW heater element then the Ia will be, worst case, 5 times the rating of the MCB. In this case is likely to be 16A times 5 = 80A ( most likely 50A) which will require an overall resistance of between 4.6 - 2.8 Ohms. However, if the simultaneously accessible metalwork is next to a 10.5kW instantaneous water heater then the likely fault current will be in the order of 0.9 Ohms. These are the worst cases which is why a 0.05 Ohms value is used to ensure that there is a minimum measurable resistance value between pipework .

This maybe true for disconnection times but doesn't explain, or doesn't prove that the voltage on the pipework will be below 50V.

Now apply the fault current to the maximum touch voltage allowed and we get a maximum resistance of 50/80 = 0.625 Ohms and for a larger load of 10.5kW we have 50/250 = 0.2 Ohms.

I would have thought somebody would have noticed that ! It must be the weekend when all go to sleep :)
 
doesn't explain, or doesn't prove that the voltage on the pipework will be below 50V.
its not meant to its to ensure there isnt a difference of 50v between any pipepwork.



Protective bonding, purpose to ensure in the event of a fault all exposed/extraneous conductive parts will be live at same potential, in order to achieve this it is recomended that the resitance of the conductor does not exceed 0.05ohms.
 
0.05 Ohms is what we might call a rule of thumb. It doesn't have to be that value as long as the resistance between simultaneous metal parts is no larger than 50/Ia (type B MCB) for the largest local load. Which for a lighting circuit might be 1.67 Ohms and for a 10.5kW instantaneous water heater 0.2 Ohms.
 
to achieve this it is recomended that the resitance of the conductor does not exceed 0.05ohms

apart from that the formula relates to the sizing of supplementary bonding conductors where disconnections times can not be met we are not talking about supp bonds but main bonds which is to ensure no difference in potential will occur between parts.
 
Last edited by a moderator:
to achieve this it is recomended that the resitance of the conductor does not exceed 0.05ohms

apart from that the formula relates to the sizing of supplementary bonding conductors where disconnections times can not be met we are not talking about supp bonds but main bonds which is to ensure no difference in potential will occur between parts.

Lol, I suppose we are not talking about cross bonding then? Where did the disconnection times not being met come from?
I thought we are discussing the effectiveness of supplementary (cross) bonding to clamp the voltage below the maximum touch voltage even when disconnection times are met and where a fault might occur.

However, It is unlikely that cross bonding would be required for normal locations that are not within a bathroom. As long as the main protective bonding is in place and the disconnection times were met which is likely to be a lot less than 0.4s (0.01s).
The rule of thumb for the main protective bonding is as you say is 0.05 Ohms....
 

Reply to Main Bonding and Cross Bonding question? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

  • Question
Bonding cables don't need to be insulated, other than for a short section at the end to identify them, and as long as they're 4mm2 or greater are...
Replies
1
Views
530
I like the plan. Best of luck.
Replies
6
Views
399

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top