Looking at pic that is a LPG bulk tank supply or a gas supply from a exsternal gas meter. I don't think you will find a meter in that house.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Main Bonding and Cross Bonding question? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Looking at pic that is a LPG bulk tank supply or a gas supply from a exsternal gas meter. I don't think you will find a meter in that house.
R=50/Ia. If the only electrical circuit is supplying a 3kW heater element then the Ia will be, worst case, 5 times the rating of the MCB. In this case is likely to be 16A times 5 = 80A ( most likely 50A) which will require an overall resistance of between 4.6 - 2.8 Ohms. However, if the simultaneously accessible metalwork is next to a 10.5kW instantaneous water heater then the likely fault current will be in the order of 0.9 Ohms. These are the worst cases which is why a 0.05 Ohms value is used to ensure that there is a minimum measurable resistance value between pipework .
its not meant to its to ensure there isnt a difference of 50v between any pipepwork.doesn't explain, or doesn't prove that the voltage on the pipework will be below 50V.
to achieve this it is recomended that the resitance of the conductor does not exceed 0.05ohms
to achieve this it is recomended that the resitance of the conductor does not exceed 0.05ohms
apart from that the formula relates to the sizing of supplementary bonding conductors where disconnections times can not be met we are not talking about supp bonds but main bonds which is to ensure no difference in potential will occur between parts.