reg 544.1.2 (BRB) (still waiting for my LGB) states "as near as practicable to the point of entry of that service into the premises"
So here we go, doing a partial rewire upgrade of circuits etc, new gas main coming in, from out the external box chased in to the wall up in to the loft (bungalow) so i have bonded as soon as it enters the loft, as nowhere else leaves access to T&I, as far as i was aware this is fine, still getting readings of .02ohms (within the .05ohms asked for) along the entire pipe.
no it all comes to commission the boiler today, i'm wrong it HAS to be within 600mm of entry?
what are your thoughts guys?
Many thanks
Danny
So here we go, doing a partial rewire upgrade of circuits etc, new gas main coming in, from out the external box chased in to the wall up in to the loft (bungalow) so i have bonded as soon as it enters the loft, as nowhere else leaves access to T&I, as far as i was aware this is fine, still getting readings of .02ohms (within the .05ohms asked for) along the entire pipe.
no it all comes to commission the boiler today, i'm wrong it HAS to be within 600mm of entry?
what are your thoughts guys?