so where's the bloody gas meter then? outside the house, under the floor, below the CU?

Believe the gas meter is outside house.
also I do understand 600mm rule but where it comes into house its to be buried so not accessable where it comes in to property.
so guessing will have to find out route of main gas pipe and then when it becomes extraneous bond there then to met.
 
Believe the gas meter is outside house.
also I do understand 600mm rule but where it comes into house its to be buried so not accessable where it comes in to property.
so guessing will have to find out route of main gas pipe and then when it becomes extraneous bond there then to met.

Bond the consumer side of the gas pipe at the meter and pass the cable through the wall to your MET.
I've seen one those guides (by ESC or the like) which shows this. I'll post it up if I can find it.

Guidance Notes 8 135.jpgGuidance Notes 8 136.jpg

GN8, where else?!
It should be made mandatory that every electrician should own a copy. :-)
 
Last edited by a moderator:
Well Archey, shouldn't you get a new version of GN8.
The only problem that I have with your suggestion, is that the pipe work will then be buried after the bond, and I'm not certain that it would be possible to confirm that the part of the pipe that enters the property will be at the same poential as where the bond is made at the meter.
 
Well Archey, shouldn't you get a new version of GN8.
The only problem that I have with your suggestion, is that the pipe work will then be buried after the bond, and I'm not certain that it would be possible to confirm that the part of the pipe that enters the property will be at the same poential as where the bond is made at the meter.

Spin, I will when it gets released, that is the latest version, next one will be a while yet.

You could easily confirm continuity with your meter and a wander lead.

I wish people would post pictures or at least a drawing of the areas they're looking at, it'd make it so much easier to give advice, hard work doing it blind.
 

Reply to the thread, titled "Main Bonding question?" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top