J

jase31

Should the MET be the earth point in the CU, with a separate single cable (10mm) run to gas, and electric meter, or could the MET be 8 way earth block on the meter board with a 10mm cable run to consumer unit, and water stop tap.

Should the CU be connected by a 10mm, 16mm, 25mm earth cable on a small domestic supply.
 
Should the MET be the earth point in the CU, with a separate single cable (10mm) run to gas, and electric meter, or could the MET be 8 way earth block on the meter board with a 10mm cable run to consumer unit, and water stop tap.

Should the CU be connected by a 10mm, 16mm, 25mm earth cable on a small domestic supply.

Either scenario is acceptable with regard to position of the MET but the sizing is subject to calculation or selection, depending on the earthing system in use. 542.3.1 and Section 543.

For PME, check 544.1.1 too.
 

Reply to Main bonding requirements - where is the MET in the Talk Electrician area at ElectriciansForums.net

Similar Threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
521
loz2754
L
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
Replies
24
Views
1K
I like your way of thinking.
Replies
6
Views
490
loz2754
L
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks