Hi.
A brief history of myself: Self employed tradesman since 1982 ( Decorating, Joinery, Plumbing ).
Done lots of minor works over the years.
Did 2382 last year. Looking to register with NIC EIC.

I'm doing a PIR on my son's ground floor flat with a view to fitting new CU.
This is what I have found so far:

Metal socket switch plates not earth.
No evidence of supplementary bonding in bathroom.
Metric & Imperial throughout.
3 core & earth to bathroom wall light.
Unused N in bedroom light switch which operates lounge wall lights also.
Son's gas meter is bonded ( bonded to silver flexible pipe not copper!) but 10mm earth runs to upstairs flat. No bonding from upstairs flat to upstairs flat gas meter!!
Only water mains bonding in MET of my sons flat.
Fuse box is Memera 3 BS 5486 80 AMP MAX. Serves lights, cooker, and sockets.

The metal socket switch plates is no problem.
Bathroom bonding will be solved with RCCB and good test results.
Presume 3 core & E is all contractors had when running cable.
Not sure about spare N in bedroom socket ( will this effect 6amp CB? )
My initial reaction to gas bonding was horror ( I know it's not to BS 7671 ).

How do I comment on all this in PIR comments section ( C1, 2, or 3 ? )?

Would be grateful for advice from more experienced Electrician.
 

Attachments

  • [ElectriciansForums.net] Main Bonding to another property.
    pics 007.jpg
    88.8 KB · Views: 66
  • [ElectriciansForums.net] Main Bonding to another property.
    pics 009.jpg
    144.9 KB · Views: 73
  • [ElectriciansForums.net] Main Bonding to another property.
    pics 010.jpg
    111 KB · Views: 73
  • [ElectriciansForums.net] Main Bonding to another property.
    pics 011.jpg
    108.3 KB · Views: 68
I personally think the whole place needs a rewire.

That spare N in Bathroom, if I comes into contact with a Live it will blow the fuse with a bit of luck
Make sure the main gas and water pipes are bonded where they enter the building as a min
Fuse box needs changing as you said
Socket back box is not a big problem as long as an earth is connected to the switch, it will provide some earth to the back box when the face is fitted - how much will depend on the quality of the metal (rusted/corroded or not) - not the best though

As you probably know you need NICEIC to do the CU change and rewire - good one to use on your assessment tbh - (Not forgetting you need 1 job for NICEIC Domestic and 3 for Commercial)


Good luck
 
I personally think the whole place needs a rewire.

That spare N in Bathroom, if I comes into contact with a Live it will blow the fuse with a bit of luck
Make sure the main gas and water pipes are bonded where they enter the building as a min
Fuse box needs changing as you said
Socket back box is not a big problem as long as an earth is connected to the switch, it will provide some earth to the back box when the face is fitted - how much will depend on the quality of the metal (rusted/corroded or not) - not the best though

As you probably know you need NICEIC to do the CU change and rewire - good one to use on your assessment tbh - (Not forgetting you need 1 job for NICEIC Domestic and 3 for Commercial)


Good luck

Niceic, elecsa, napit, BSI, stroma . Might be another.
 
Is it the switch plate that is not earthed or the KO box? Can you describe the unused neutral some more? Supplementary bonding is not required if you sort the main bonding and install RCD protection. Presumably this is a converted house and the flats share a gas main. However there should be main bonding dedicated to each flat. This should be no more than 600mm from where the service enters the property, before any branches and the clamp should be attached to solid not flexible pipe. Mostly C2 or C3 as there is not imminent danger but if it is the socket outlet plate not earthed then take care of it asap.
 
Hi Mark.
Just the back boxes, so not a problem. It's the main bonding that is freaking me out. Each flat has independent gas supply yet there is only main bonding to one meter and that's coming from upstairs flat but bonded to my son's gas meter supplying his flat downstairs!
I know I will have to run new 10mm E to son's gas meter and take existing E over to black Gas Meter but I can't work out who is bonded and who is n't!
I have checked that extraneous central heating pipe work in my son's flat is not connected to upstairs flat in any way.

The bedroom switch would have been a 1 gang then changed to a 2 gang hence cable on wall going into switch ( has used short 3cm 1.5mm linking common to common hence spare N ).

Thanks again.
 

Attachments

  • [ElectriciansForums.net] Main Bonding to another property.
    001.jpg
    140.5 KB · Views: 35

Reply to Main Bonding to another property. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
865

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top