sparkygg

This is my first post and hoping someone can help?

Just wired an external combi oil boiler. I ran a 10mm bond from CU to the incoming pipes which are all 22mm and 28mm copper. They come through the wall from outside and I have put an earth bonding clamp on each pipe and looped the bond between them all. Now I am not sure if I should have run the bond out to the oil line entering the boiler? It comes through the ground for 20m or so and pops up just beside the boiler which is mounted on a paving slab plinth. The oil pipe doesn't enter the building and as i said any metal pipes which do are now bonded. The incoming water is in blue polypipe and is bonded where it turns to copper further into the installation. What should I have bonded? I am confused!

Any guidance would be appreciated.
 
Sounds OK to me, working on the theory that we bond gas on the consumers side of the meter, so you have bonded the pipes on your set up on the consumer side of the installation. I did something similar with gas tanks recently.

Cheers.........Howard
 
Just to let you know I had my Elecsa inspection on Wednesday and this job was one that Paul chose to view. Showed him that I had "cross bonded" all metal work entering the house all looped off the main bond to the incoming water with out any breaks. He said this was fine and if I had bonded outside to the oil I would have actually been extending the equipotential zone which would have worsened the situation. So I guess if you have done what I did you will be ok, but still a bit of a grey area in my view.

Thanks for the response its always good to know when think you may have done right but not 100% sure.
 
i had my inspection with elecsa today. he said he would like to see a bond on the external oil pipe connecetd to the external boiler, gray area with them to.

IMO this should be bonded if the incoming pipe to the oil boiler is copper as this would introduce and earth potential into the house. It does say on the certificate bonding-other services.
 
There is no requirement to bond the oil pipe to an external oil fired boiler as it cannot introduce a potential into the property. As long as the water supply pipe to the property is bonded to the MET and if there is <0.05 ohms continuity between the MET and the heating service pipes at the boiler (as is usually the case due an all metal manifold) then there is no need to supplementary bond these either.
 
Last edited by a moderator:
There is no requirement to bond the oil pipe to an external oil fired boiler as it cannot introduce a potential into the property. As long as the water supply pipe to the property is bonded to the MET and if there is <0.05 ohms continuity between the MET and the heating service pipes at the boiler (as is usually the case due an all metal manifold) then there is no need to supplementary bond these either.

Didn't think there was a supply water pipe to the boiler! How silly. Yeah Markie's right. ;)
 
Basically as long as all pipes entering the property are bonded this is ok. I even rang the Niceic tech support line that my mate belongs to, and they say not to bond the oil if its external and never enters the building.

Be nice if the Elecsa inspectors could agree though!

thanks for all your replies.

Sparky GG
 
I agree really that u shouldn't bond the oil if it never enters The building as it would be at a different potential to outside the idea of bonds i thought was to bring everything extraneous to The same potential in case of a fault or a difference in potential ? I would like to here a electrical council advice as they cover us ?
 
Just to let you know I had my Elecsa inspection on Wednesday and this job was one that Paul chose to view. Showed him that I had "cross bonded" all metal work entering the house all looped off the main bond to the incoming water with out any breaks. He said this was fine and if I had bonded outside to the oil I would have actually been extending the equipotential zone which would have worsened the situation. So I guess if you have done what I did you will be ok, but still a bit of a grey area in my view.

Thanks for the response its always good to know when think you may have done right but not 100% sure.

Why would extending the equipotential zone worsened the situation?? I take it you have an electrical supply to this boiler which is being supplied with oil from an underground metallic pipe ...Right?? So the equipotential zone ''Needed'' to be extended didn't it!!!

What is the oil tank construction, ...metal or non-metallic?? How is the oil tank filled, ...via a filling pipe extending to the property boundary, or via a filling attachment close to the tank?? If these are metallic, then they need to also be ''Earthed'', as the filling tanker will need a connection point for his oil tankers equalisation extension lead.
 
Why would extending the equipotential zone worsened the situation?? I take it you have an electrical supply to this boiler which is being supplied with oil from an underground metallic pipe ...Right?? So the equipotential zone ''Needed'' to be extended didn't it!!!

What is the oil tank construction, ...metal or non-metallic?? How is the oil tank filled, ...via a filling pipe extending to the property boundary, or via a filling attachment close to the tank?? If these are metallic, then they need to also be ''Earthed'', as the filling tanker will need a connection point for his oil tankers equalisation extension lead.

I'll take issue with this.
It is not possible to have an 'equipotential zone ' in an external situation...(such as surrounding an external boiler).....in such a situation the boiler is surrounded by the general mass of earth so it would be pointless trying to create an equipotential zone by bonding the oil line.
The equipotential zone is in the building , and the heating pipes coming from the boiler introduce an earth potential...(possibly from the oil line)....therefore it is correct to main bond the heating points at the point of entry.
 
To my mind, if the oil pipe is considered an extraneous-conductive-part, it will require bonding.
If the boiler is within the building, the oil pipe will require bonding as close as practicable to where it enters the building, preferably within 600mm.
If the boiler is in another building, then it may be that it should be treated as a separate installation, and will require it's own earthing and bonding arrangements (i.e. TT).
In any event the oil pipe should be bonded.
 

Reply to main bonding to external boiler. in the Australia area at ElectriciansForums.net

Similar threads

  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K
I
  • Article
Water hammer/noise from pipework at night? I attended a Job where the customers complained about noisy pipes more often late at night bur...
Replies
0
Views
180
Illuminate
I

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top