Have kind of over thought this one until I'm not sure any more! Input welcome.
Have been installing a supply to a machine, and gathering the necessaries for the EIC today I noted that the bonding is undersized. It's a 400a incomer with 185mm tails into an MCCB panel DB. TNCS....and main bonding to water,gas and steel is in 25mm. Table 54.8 gives a minimum CSA of 50mm where the supply neutral is over 150mm. Where I've started to doubt my initial assessment is that I've taken the tails as the benchmark for the supply neutral size....or should it be the DNO incomer neutral CSA which I cannot confirm? Been a long day and I'm not thinking straight.
It matters because it is an installation newly constructed 5 years ago, and a recent EICR by another contractor didn't flag any issues with bonding. Don't want to look a dick and flag up a non-issue.
Have kind of over thought this one until I'm not sure any more! Input welcome.
Have been installing a supply to a machine, and gathering the necessaries for the EIC today I noted that the bonding is undersized. It's a 400a incomer with 185mm tails into an MCCB panel DB. TNCS....and main bonding to water,gas and steel is in 25mm. Table 54.8 gives a minimum CSA of 50mm where the supply neutral is over 150mm. Where I've started to doubt my initial assessment is that I've taken the tails as the benchmark for the supply neutral size....or should it be the DNO incomer neutral CSA which I cannot confirm? Been a long day and I'm not thinking straight.