Sorry if this has been covered before. Went to a job today to wire a heating system and the install requires main bonding. The problem is that I can't get to the main board as its solid floors etc. There is a sub main feeding a db upstairs supplied by a 16mm twin. Can I run my 10mm earths to this sub board
? TNC-S earthing. Please be gentle!!
 
If its 16mm twin and earth then i would say no as the earth is not a large enough conductor size to be used as a combined earthing and bonding conductor back to the met

Tim
 
Need to wire a supply for heating and an immersion. Will be replacing the main db and various other works so will need to wire main bonders. Place is a bit of a shambles to be fair... No cpc's in downstairs lights , exposed parts in db's etc, might end up being there a while!
 
Need to wire a supply for heating and an immersion. Will be replacing the main db and various other works so will need to wire main bonders. Place is a bit of a shambles to be fair... No cpc's in downstairs lights , exposed parts in db's etc, might end up being there a while!

I'd say as it's a bit more than just wiring the heating system you should be ensuring all bonding meets current regulations along with all other work you undertake. IMO
 
There is something on the ESC website re being able to use 6mm as long as there are no signs of thermal damage etc etc. However IMO you are installing new circuits and replacing a DB so I would be looking at installing a new main earth and bonding conductors as per table 54 (7 or 8) can't remember due to it being TNC-S. So if the DNO neutral is 35 mm or less then Im afraid its going to have to be 10mm !! I take it there is extraneous parts where you are doing the work!
 
Last edited:
There is something on the ESC website re being able to use 6mm as long as there are no signs of thermal damage etc etc. However IMO you are installing new circuits and replacing a DB so I would be looking at installing a new main earth and bonding conductors as per table 54 (7 or 8) can't remember due to it being TNC-S. So if the DNO neutral is 35 mm or less then Im afraid its going to have to be 10mm !! I take it there is extraneous parts where you are doing the work!

Think you'll find that only refers to leaving ''Existing'' 6mm main bonding cables in place, not that you can install 6mm MB cables where it calls for 10mm...
 

Reply to Main bonding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
856
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K
  • Question
OP - is this T&E run on the surface or in conduit all the way? Or is any of it below the surface? I'm guessing not as you were talking about...
2
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top