I had a look at g83/2 and thought it was sufficiently vague that provided:
- there is a downstream mcb to provide overload protection
- the prospective fault current at the downstream mcb was enough to blow the suppliers fuse
then it meets g83/2 and 7671.
But there is a serious risk that a single 2.5mm conductor will not be gripped properly in the input terminals of a standard cu main switch when alongside say a 25mm conductor
- there is a downstream mcb to provide overload protection
- the prospective fault current at the downstream mcb was enough to blow the suppliers fuse
then it meets g83/2 and 7671.
But there is a serious risk that a single 2.5mm conductor will not be gripped properly in the input terminals of a standard cu main switch when alongside say a 25mm conductor