Hey guys, I'm getting a bit confused with regards to the regs for the sizing of bonding/main earth. Anyone able to shed some light on the regs or point me to the exact one?...

I'm feeling my way here, but isn't the CSA of an earth usually 67% smaller than that of the conductors it's earthing?
 
I think you are mixing up the size of the CPC which is incorporated in twin and earth cable as the CPC is generally smaller than the main conductor.

IE 2.5 twin & earth has a has the main condutor of 2.5mm and the Cpc 1.5 mm.

2.5/1.5 =1.67 ratio

4.0/1.5= 2.67

6.0/2.5=2.4

Etc

However 1mm twin & earth is 1mm/1mm so its the same.

The CPC has to be large enough to carry the fault current which could flow in the event of a fault to disconnect the protective device in the required time.

Hope this makes sense.
 
I think you are mixing up the size of the CPC which is incorporated in twin and earth cable as the CPC is generally smaller than the main conductor.

IE 2.5 twin & earth has a has the main condutor of 2.5mm and the Cpc 1.5 mm.

2.5/1.5 =1.67 ratio

4.0/1.5= 2.67

6.0/2.5=2.4

Etc

However 1mm twin & earth is 1mm/1mm so its the same.

The CPC has to be large enough to carry the fault current which could flow in the event of a fault to disconnect the protective device in the required time.

Hope this makes sense.

You've got some of your ratios mixed up there Tony :)


Regards Chris
 
Also, this talk of 'main earth' and 'bonding' does not do any new readers any favours, they are not the terms used now, so we should be using 'earthing conductor',* 'main protective bonding conductor' and 'supplementary bonding conductor', as well as 'circuit protective conductor'.
 

Reply to Main earth and bonding csa? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
668
loz2754
L
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
514

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top