On a domestic tns suppy what do you class as your main earth onto test sheets? As I have a unsheathed 2.5 from sheath to earth block then 16mm to db. Get fine ze readings. Would you record it as 2.5?
 
But do still do the calculation to establish whether said bit of 2.5 is ok or not.
And I'd hazard a guess that it'll be an imperial size cable rather than metric.
 
Record what comes from the MET to the DB. You don't record the size of the distributor tails going to the meter do you.

Have to disagree with this i'm afraid, earthing conductor is from the means of earthing to the MET
 
Last edited by a moderator:
debatable point. we should ask niceic who will then come up with a 20 page fact sheet which will say nowt.
 
Have to disagree with this i'm afraid, earthing conductor is from the means of earthing to the MET
wrong the MET in domestic is within the ccu so thats what you write down.

the core coming of the pilc doesnt go straight toto board and is not your problem, if the external loop impedance is too high its in the hands of the supplier
 
I'm with the other Andy on this.
The earthing conductor is the conductor between the means of earthing and the MET. If the MET is in the CU then you only have one conductor anyway. If the MET is external to the CU, then the conductor between the CU and MET is really a CPC.
 

Reply to Main earth tns in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
529
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
916

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
505
You would treat it as a TT installation.
2
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top