M

miLarKey

Hi,

I have recently carried out a periodic test and inspection on 1960s purpose built flat. The means of earthing was via the main gas pipe connected by earth clamp before the gas meter.
Is this acceptable under BS 7671 2008? I had a Ze reading on 0.19 ohms.
 
542.2.4 says no

metallic pipe work used for water supply maybe used if precautions are taken against its removal
 
Last edited by a moderator:
Hi,

I have recently carried out a periodic test and inspection on 1960s purpose built flat. The means of earthing was via the main gas pipe connected by earth clamp before the gas meter.
Is this acceptable under BS 7671 2008? I had a Ze reading on 0.19 ohms.

Are you serious??
Just to clarify Kinky's post ,it is not acceptable to use a public water supply pipe as a means of earthing.Only private pipes may be used as an earth electrode with the precautions stated above.
 
Last edited by a moderator:
Hi,

I have recently carried out a periodic test and inspection on 1960s purpose built flat. The means of earthing was via the main gas pipe connected by earth clamp before the gas meter.
Is this acceptable under BS 7671 2008? I had a Ze reading on 0.19 ohms.

Thats a wind up isnt it , surely ?
 
Hi,

I have recently carried out a periodic test and inspection on 1960s purpose built flat. The means of earthing was via the main gas pipe connected by earth clamp before the gas meter.
Is this acceptable under BS 7671 2008? I had a Ze reading on 0.19 ohms.

Surely that's a wind up, though.

If the DNO gave him TN-C-S now, with the regulation 0.35 Ze, and he bonded that gas pipe (as you do:)) - most of the installation's current is going to be flowing down that gas pipe.

Or am I missing something??
 
Wayne the tncs will probably [but not always] be less than 0.35 ,and there will always be the case of parrallell paths to extraneous conductive parts in the event of a fault to earth, so i dont think that is a major issue. the issue is not having a suitable earthing facility at present. Must say though that if the op has to ask the question then maybe he should consider some training, cos its a fundamental part of I & t to know the answer.

sparkylad.
 
Wayne the tncs will probably [but not always] be less than 0.35 ,and there will always be the case of parrallell paths to extraneous conductive parts in the event of a fault to earth, so i dont think that is a major issue. the issue is not having a suitable earthing facility at present. Must say though that if the op has to ask the question then maybe he should consider some training, cos its a fundamental part of I & t to know the answer.

sparkylad.

My thoughts exactly.....If you have to ask whether it is acceptable to use a gas pipe as a main earth you do not have sufficient knowledge to be carrying out a PIR.
 
Wayne the tncs will probably [but not always] be less than 0.35 ,and there will always be the case of parrallell paths to extraneous conductive parts in the event of a fault to earth, so i dont think that is a major issue. the issue is not having a suitable earthing facility at present. Must say though that if the op has to ask the question then maybe he should consider some training, cos its a fundamental part of I & t to know the answer.

sparkylad.

Yeh, my point was that it seemed awfully low - surely that's not the kind of reading I'd get if I did a Ze test on my gas pipe.

Let's take a good TN-C-S system with a Ze of 0.19 ohms - are you telling me that a bonded gas pipe would offer the same impedance back to the transformer as the supply neutral conductor connected to the star point?:)

Either there is another means of earthing or he's measured it wrong...... or it's a wind up

I wasn't talking about an earth fault, by the way.

I was talking about the normal operating current taking this path as oposed to travelling down the neutral(of higher impedance)
 
Last edited by a moderator:
Oh. Got you now wayne ..sorry , yes I get the point you are making, and yes the op unfortunately does not inspire great confidence in his I & T ing prowess so he may well indeed missed some other means of Earthing or Bonded Extraneous part such as a mettallic water pipe etc.
 
Your sure that is the main earth to the flat?

Have you tried to do a Ze on the remaining earths in the MET? I can understand older houses having relied on the use of a Metal pipe for an earth but a 1960s flat? What floor was the flat on and was there a communal cupboard with the main incoming supply for the building in there?
 
Yeh, my point was that it seemed awfully low - surely that's not the kind of reading I'd get if I did a Ze test on my gas pipe.

Let's take a good TN-C-S system with a Ze of 0.19 ohms - are you telling me that a bonded gas pipe would offer the same impedance back to the transformer as the supply neutral conductor connected to the star point?:)

Either there is another means of earthing or he's measured it wrong...... or it's a wind up

I wasn't talking about an earth fault, by the way.

I was talking about the normal operating current taking this path as oposed to travelling down the neutral(of higher impedance)

It could be that he was measuring a gas bond with a common pipe to other flats and the reading of 0.19 was via the other flats gas bond to their met
 

Reply to Main earthing by gas pipe. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
661
loz2754
L
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top