Hi,
I have recently carried out a periodic test and inspection on 1960s purpose built flat. The means of earthing was via the main gas pipe connected by earth clamp before the gas meter.
Is this acceptable under BS 7671 2008? I had a Ze reading on 0.19 ohms.
542.2.4 says no
metallic pipe work used for water supply maybe used if precautions are taken against its removal
Hi,
Are you serious??
Just to clarify Kinky's post ,it is not acceptable to use a public water supply pipe as a means of earthing.Only private pipes may be used as an earth electrode with the precautions stated above.
Hi,
Thats a wind up isnt it , surely ?
Hi,
Surely that's a wind up, though.
If the DNO gave him TN-C-S now, with the regulation 0.35 Ze, and he bonded that gas pipe (as you do:)) - most of the installation's current is going to be flowing down that gas pipe.
Or am I missing something??
Wayne the tncs will probably [but not always] be less than 0.35 ,and there will always be the case of parrallell paths to extraneous conductive parts in the event of a fault to earth, so i dont think that is a major issue. the issue is not having a suitable earthing facility at present. Must say though that if the op has to ask the question then maybe he should consider some training, cos its a fundamental part of I & t to know the answer.
sparkylad.
sparkylad.
My thoughts exactly.....If you have to ask whether it is acceptable to use a gas pipe as a main earth you do not have sufficient knowledge to be carrying out a PIR.
sparkylad.
Yeh, my point was that it seemed awfully low - surely that's not the kind of reading I'd get if I did a Ze test on my gas pipe.
Let's take a good TN-C-S system with a Ze of 0.19 ohms - are you telling me that a bonded gas pipe would offer the same impedance back to the transformer as the supply neutral conductor connected to the star point?:)
Either there is another means of earthing or he's measured it wrong...... or it's a wind up
I wasn't talking about an earth fault, by the way.
I was talking about the normal operating current taking this path as oposed to travelling down the neutral(of higher impedance)
Oh. Got you now wayne ..sorry , yes I get the point you are making, and yes the op unfortunately does not inspire great confidence in his I & T ing prowess so he may well indeed missed some other means of Earthing or Bonded Extraneous part such as a mettallic water pipe etc.
Your sure that is the main earth to the flat?
Have you tried to do a Ze on the remaining earths in the MET? I can understand older houses having relied on the use of a Metal pipe for an earth but a 1960s flat? What floor was the flat on and was there a communal cupboard with the main incoming supply for the building in there?
It could be that he was measuring a gas bond with a common pipe to other flats and the reading of 0.19 was via the other flats gas bond to their met
This was my thinking - That's why I am wondering where the main incoming supply is. Whether there is one main supply cable split to individual meters for each flat or if they all have individual cables. Round my way especially its unusual to get flats that all have an individual supply cable coming into them. They normally have one massive supply cable that feeds meters for each flat (That probably makes very little sense to people reading but its clear in my head!).
A gas pipe or water pipe should not be used as a means of main earthing for one common sense reason, the same reason the behind the BRB regulation. Irrespective of whether you get a good Ze measurement or not you can't guarantee that this will always be the case because water/gas companies can and do disrupt/upgrade their supply pipe. ie to plastic pipes
Lol, but was rewired in 1968 by YEB using the same regs I fear. Meter board was held against wall of cellar by a 4" x 4" chump of wood jammed in there.
Possibly not - owned a house in Leeds from the Victorian era where main earth was gas pipe - clamped on the customer side of the meter too....
Had similar thing in my house. There was no earthing conductor.
Only path to earth for the entire property was via the bonds to gas & water mains.
Gas bond was after the meter andf the incoming water was plastic.
o dear
Huh? Why would any current other than slight leakage be flowing in the earth in normal operating circumstances?
Both conductors are going to be completely separate upstream until you hit the supply in a TN-C-S system, so surely unless you have a neutral-earth short circuit then there would be no path for the current to get on the earth? :)
But if you bond the gas pipe (with the 0.19 ohm Ze) to the MET, the MET is connected to the neutral at the service head.
So when the normal operating current of the installation flows down the neutral to the service head, it has a choice of path back to the transformer......down the neutral (Ze 0.35) or down the Earthing conductor/Bonding conductor/gas pipe (Ze 0.19).
Where do you think most of it will go?:)
This is why losing the supply neutral on a PME (PEN) system is so worrying.
And this is why I said 0.19 was awfully low for a gas pipe.
You will always get some current flowing down the parallel paths, but it shouldn't be anywhere near that amount.:)
Hmm, I like you, you make me think!! :D
I doubt very much that the earth is actually 0.19 ohms, as it is just a large earth electrode, so methinks the test has been wrong or this is due to parallel paths somehow...
I agree with losing the neutral on a PME supply, but that's why it's an ME and not just an E.
I think Des probs hit the nail on the head with post #15
*******Removed******* I knew it wasn't acceptable for BS7671:2008 but the wiring was over 60 years.
So you haven't been around for nearly 3 years, and come back having a rant at a respected member, for making what was a valid observation!!
See you in another 3 years then!! lol!!
I have been around I have just had better things to do then spend time on here. I am in a band now that is doing very well and I only found your quote as I was carrying out a google search for something else. I am so glad I do not have work in the electrical/building trade any more. You my be a respected member on here but you a definitely not respected by me.
*********Removed********
Btw to all you other members re the gas pipe, it was a very old 3" in diameter one that was in a 1930's purpose built flat in London. This is why I think the readings were low due to the size of it and parallel paths. Thank you to all of you that responded to me in a helpful manner.
Foul language and abusive posts aren't tolerated.
i,m surprised a 30 day ban has not been made. marvo, you must be in a good mood. :chillpill:
Just as well you're out of the industry, if you actually left the installation as was, without a primary means of main earthing!!
In a Band now eh, so now probably on a constant high, on wacky baccy or stronger, .....another flash in the pan musician that think what they have to say, is somehow more important than any others opinion!! lol!!
Main earthing by gas pipe.
miLarKey,
Mpe123,