Domestic TNCS, main earthing conductor runs to water pipe, bonds via clamp with label, cable is continuous, then runs on to MET in DB.

Seems wrong, but cant find specific reg to say so....any thoughts?

Thanks,

Timotei
 
Its an earthing conductor not a main protective bonding conductor. Part 2 definitions. Fig 2.1.

But I can't see anything specifically prohibiting it.
 
I think @Wilko has it with the Ze problem. And looking at 542.4.1 (18th) it states an MET shall be provided...
and at 542.4.2 ...To facilitate measurement of the resistance of earthing arrangements...
So checking bonding requirements and Ze would be a bit of a conundrum and it could be argued unless there is separate MET complying with the former reg. then it would not comply?
 
I think @Wilko has it with the Ze problem. And looking at 542.4.1 (18th) it states an MET shall be provided...
and at 542.4.2 ...To facilitate measurement of the resistance of earthing arrangements...
So checking bonding requirements and Ze would be a bit of a conundrum and it could be argued unless there is separate MET complying with the former reg. then it would not comply?
I have agreed with you, though if the clamp to the water pipe is easily accessible and the conductor is continuous then measuring the Ze may not be a major problem. Not ideal though, I agree. I would definitely look at running in a separate conductor, just in case wet pants comes along and does some pipework alteration and decides to just cut through the cable.
 

Reply to Main earthing Conductor also bonds water in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
668
loz2754
L
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top