I know main bonding to water and gas need to be 0.05 ohms

But what about the main earthing conductor?

Does it have a maximum resistance value from MET to the CU?
 
Last edited:
In practical terms assuming you have a CU very near the MET the resistance should be almost negligible, so if Zs@DB is measured it would be well under the max Ze figures of 0.35 (TNCS) and 0.8 (TNS).
It sounds as though this question relates to a particular situation and maybe more details would help.
 
Nope.
GN3 refers to a measurement made between the cable connected to the bonding clamp, and the actual pipe. This reading to be <0.05 ohms. There is no regulation specifically mentioning a maximum resistance of any bonding conductor.
lots of sparks get this wrong. the 0.05 is as you say. absofruitly nothing to do with the resistance of the bonding conductor.
 
it's to ensure that :

1. the bonding clamp is securely connected to the metal of the pipe, not through paint.

2. wet-pants hasn't fitted clamp to a plastic pipe.seen that done a couple of times.
 
In practical terms assuming you have a CU very near the MET the resistance should be almost negligible, so if Zs@DB is measured it would be well under the max Ze figures of 0.35 (TNCS) and 0.8 (TNS).
It sounds as though this question relates to a particular situation and maybe more details would help.
Not situational I have just seen a really long 16mm earthing conductor today on a tncs a few days ago and was just wondering if it had a maximum length
 
Yes they were fused at an isolator
So would it be fair to say that the main earthing conductor only runs as far as the fused switch and from there on it becomes a cpc which has to meet the max Zs requirements of the fuse in the isolator which in turn dictates its max resistance?
 
Noting that one has to be careful to define where the MET is, according to what is connected where. E.g. if the MEB conductors terminate in the CU, the cable from the origin to the CU is not just a CPC.
 

Reply to Main Earthing conductor max resistance? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
673
loz2754
L
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top