I know main bonding to water and gas need to be 0.05 ohms

But what about the main earthing conductor?

Does it have a maximum resistance value from MET to the CU?
 
Last edited:
In practical terms assuming you have a CU very near the MET the resistance should be almost negligible, so if Zs@DB is measured it would be well under the max Ze figures of 0.35 (TNCS) and 0.8 (TNS).
It sounds as though this question relates to a particular situation and maybe more details would help.
 
Nope.
GN3 refers to a measurement made between the cable connected to the bonding clamp, and the actual pipe. This reading to be <0.05 ohms. There is no regulation specifically mentioning a maximum resistance of any bonding conductor.
lots of sparks get this wrong. the 0.05 is as you say. absofruitly nothing to do with the resistance of the bonding conductor.
 
In practical terms assuming you have a CU very near the MET the resistance should be almost negligible, so if Zs@DB is measured it would be well under the max Ze figures of 0.35 (TNCS) and 0.8 (TNS).
It sounds as though this question relates to a particular situation and maybe more details would help.
Not situational I have just seen a really long 16mm earthing conductor today on a tncs a few days ago and was just wondering if it had a maximum length
 
Noting that one has to be careful to define where the MET is, according to what is connected where. E.g. if the MEB conductors terminate in the CU, the cable from the origin to the CU is not just a CPC.
 
So would it be fair to say that the main earthing conductor only runs as far as the fused switch and from there on it becomes a cpc which has to meet the max Zs requirements of the fuse in the isolator which in turn dictates its max resistance?
Maybe, maybe not:
  • It has to allow the fused-switch to meet its Zs for 5s disconnection at the end of the sub-main (as you just said).
  • It has to allow all final circuits to meet the Zs requirement.
  • It has to meet the adiabatic limit for all OCPD clearing (supply fuse & finals circuits, but obviously they will be smaller and can be ignored if supply is met)
  • And also any possible extraneous bonding on TN-C-S (which ought to be back to the MET, but if sub-main to the remote board, such bonds might well be connected there) so you might have the (typically) 10mm minimum.
If you have no reason to doubt the design, then the resistance check is basically to verify it is working as designed, so based the GN3 figure would be:
R measured <= 0.05 + expected cable R2
 
So would it be fair to say that the main earthing conductor only runs as far as the fused switch and from there on it becomes a cpc which has to meet the max Zs requirements of the fuse in the isolator which in turn dictates its max resistance?

Maybe, maybe not:
  • It has to allow the fused-switch to meet its Zs for 5s disconnection at the end of the sub-main (as you just said).
  • It has to allow all final circuits to meet the Zs requirement.
  • It has to meet the adiabatic limit for all OCPD clearing (supply fuse & finals circuits, but obviously they will be smaller and can be ignored if supply is met)
  • And also any possible extraneous bonding on TN-C-S (which ought to be back to the MET, but if sub-main to the remote board, such bonds might well be

16mm to fused isolator, then 16mm to CU
Or it might have had 16mm from the met and a separate 16mm to the isolator
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
london
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Main Earthing conductor max resistance?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16
Unsolved
--

Advert

Thread statistics

Created
dokkan1080,
Last reply from
dokkan1080,
Replies
16
Views
6,086

Advert

Back
Top