Hi

Was visiting a friends house yesterday who is having some renovation work done and I was just being nosy but came across his DB (that is due to be changed) with what looked like no main earth. There is an earth connected in the DB but it’s just cut off below the main income ( see pic)

What would people do in this case? Do the suppliers have to provide an earth or is it something an electrician would sort?

[ElectriciansForums.net] Main Earthing On DB Help
 
I’ve come across a few lately that have no Earthing conductor connection - both needed to be simply connected to TNS and I’ve no idea why they weren’t - both were picked up by trades fitting stuff 1st was a shower fitted and would commission as no earth showing - I got 0.13 once connected
2nd was the gas man not picking up on his socket tested - I let the customer see Zs at socket (though bonding) of 298 ohms and when earth terminated same Zs 0.68
Both like that for 15 to 20years - they will not be the only ones in the country either!
Not sure whether to blame other trades or the last spark in the premises!
Both customers happy at the ease of the fix and not given too much of a doom and gloom scenario until after I finished the tea and biscuits!
 
As above, isolate it and get DNO to come in. That would be the first steps in finding out.

Is this in a built up area? How old are the houses? Could be worth checking local houses to see what earthing arrangements are being used locally. If close property's are on TNC or TNCS I doubt very much this property would be TT. DNO would confirm
 
I wouldn't isolate it at all, I would bang a rod in and connect to that then ask the DNO to provide an earth, switching someones leccy off and walking away is very nice of you isn't it?
 
Ok so what if you don't have a rod to hand and you cant get one till say, Monday?

I wouldn't walk away with it energised like that.

So you would walk into someones house and turn off the electric till monday when you can get a rod? i know i wouldn't, just tell them the problem try and get the dno out to fix it and dont do any work on it till its sorted. cant go around just turning the electric off to peoples houses for days and even if you did im sure they would turn it back on some how when you left.
 
I don't see what right or authority we have to leave a dwelling without power in these circumstances. We are not the electrical police, we have no right to turn off the power supply and lock it off until we return at a later date to sort it.
You are correct. If it's bad bad bad (not had this yet) I would call DNO - I understand they have the authority to remove supply if they consider it dangerous (?).
 
Yeh I get it. Perhaps your right. However I'm not sure I'd want to be standing in the dock explaining why I left an installation energized with no effective earthing.

I suppose the best solution is to get the customer to sign something to say they understand there is no earth but would like the installation kept energized until remedial work can take place
 
Yeh I get it. Perhaps your right. However I'm not sure I'd want to be standing in the dock explaining why I left an installation energized with no effective earthing.

I suppose the best solution is to get the customer to sign something to say they understand there is no earth but would like the installation kept energized until remedial work can take place
You would only end up in the dock if you carried out an alteration or addition and left a dangerous situation.
 
Yeh I get it. Perhaps your right. However I'm not sure I'd want to be standing in the dock explaining why I left an installation energized with no effective earthing.

I suppose the best solution is to get the customer to sign something to say they understand there is no earth but would like the installation kept energized until remedial work can take place

As above mate if you have not done any work at all on it then nothing will happen to you it will be the person who did its fault not your so you would not end up in the dock
 

Reply to Main Earthing On DB Help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
I agree new CU is best or come off an MCB. A further option if you have lots of wall is to regland the SWA into a galv box, crimp onto tails with...
Replies
4
Views
2K
  • Question
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
1K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
380
  • Question
Must be thousands of installs like this. No wonder so many company’s jumped on the solar bandwagon and just threw them in. I’ll get mine changed...
    • Like
Replies
23
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks