Hi

Was visiting a friends house yesterday who is having some renovation work done and I was just being nosy but came across his DB (that is due to be changed) with what looked like no main earth. There is an earth connected in the DB but it’s just cut off below the main income ( see pic)

What would people do in this case? Do the suppliers have to provide an earth or is it something an electrician would sort?

[ElectriciansForums.net] Main Earthing On DB Help
 
I’ve come across a few lately that have no Earthing conductor connection - both needed to be simply connected to TNS and I’ve no idea why they weren’t - both were picked up by trades fitting stuff 1st was a shower fitted and would commission as no earth showing - I got 0.13 once connected
2nd was the gas man not picking up on his socket tested - I let the customer see Zs at socket (though bonding) of 298 ohms and when earth terminated same Zs 0.68
Both like that for 15 to 20years - they will not be the only ones in the country either!
Not sure whether to blame other trades or the last spark in the premises!
Both customers happy at the ease of the fix and not given too much of a doom and gloom scenario until after I finished the tea and biscuits!
 
As above, isolate it and get DNO to come in. That would be the first steps in finding out.

Is this in a built up area? How old are the houses? Could be worth checking local houses to see what earthing arrangements are being used locally. If close property's are on TNC or TNCS I doubt very much this property would be TT. DNO would confirm
 

Reply to Main Earthing On DB Help in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
844
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
967

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
492

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top