I think it was a 17th edition change but not certain
Main protective bonds should be not less that half the csa of the earthing conductor and not less than 6.0 unless PME conditions apply, this has been stated as far back as the 15th Ed when I started work. The 15th Ed never quoted a minimum size where PME conditions applied just that the electricity supplier should be consulted it was the 16th Ed that quoted 10.0 as a minimum size for PME systems.
So whilst 10.0 is considered the norm it does not apply to all systems.
There are PME systems out there with main protective bonds sized at 6.0 installed pre 16th Ed and you have no way of knowing if they were correct at the time as they would have been sized to supply company requirements.
it is, I reckon the existing 6mm that's at the stopcock which I cant get to should have been changed when the board was changed in 1994, which I believe is the 16th edition.i thought this was just to settle an argument?
The question is, does it need bonded at all? Or is it plastic water pipe coming into the property?
I trained on the 15th/16th from 1990, and I’m pretty certain I was told to run a 10mm for equipotential bonding, and 4mm for all supplemental bonding.