awarner

Morning all
I've got a lot of work coming up doing main gas bonding but its mostly going to be in commercial and industrial situations. I'll give you the following scenario.
Main DB is in building number 1, gas main comes into building number 2 on the same site. Blg 2 is fed , electrically, via a submain from bldg 1 and has its own DB.
BS7671 says that main bonding has to be taken to the MET, but in a situation such as this, is the main earthing terminal at Building 2 alright to go to or have I got to go to the lengths of getting the cable back to the MET in building 1?
Also, if the bond can be made in building 2, should the size of the bond (as per section 544 of the regs) be worked out on the mains coming into DB1 or the size of the submain going to DB2?
I'm scratching my head on this one at the moment and thanks for any advice you can give me.
 
My understanding is
The Gas,water etc hat to be bonded where it enters the building so I would bond at each entry to both buildings sizing my bond from the main incommer to each building.

Basically i woul;d trat each building as a seperate installation.

hope that helps.
 
Morning all
I've got a lot of work coming up doing main gas bonding but its mostly going to be in commercial and industrial situations. I'll give you the following scenario.
Main DB is in building number 1, gas main comes into building number 2 on the same site. Blg 2 is fed , electrically, via a submain from bldg 1 and has its own DB.
BS7671 says that main bonding has to be taken to the MET, but in a situation such as this, is the main earthing terminal at Building 2 alright to go to or have I got to go to the lengths of getting the cable back to the MET in building 1?
Also, if the bond can be made in building 2, should the size of the bond (as per section 544 of the regs) be worked out on the mains coming into DB1 or the size of the submain going to DB2?
I'm scratching my head on this one at the moment and thanks for any advice you can give me.

hi,spooky ive just completed an exact same job.i had a 95mm main incomer with a 50mm main bonding but i took a seperate 35mm bonding in2 the seperate building to my mains gas even though that had a 25mm submain supplying that building.That is If the gas supply is supplying both buildings.otherwise like that guy says treat every installation as its own.My view is so long as you label everything up and even when you fill in your certs.Also maybe fill in on a seperate attatchment to your certs stating what you have done.
good luck
 

Reply to Main gas bonding in commercial installations in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
520
loz2754
L
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
489
  • Question
Thank you, that's a really helpful post, nice & clearly stated and helps me clear up a lot of confusion on this matter.
2 3
Replies
65
Views
6K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
  • Question
investigated a little bit more today and noticed a piece of metal connected externally to the incoming head which was bolted to some copper earth...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks