How come us electricians have to put in metal Db’s,they come along & put in a plastic isolater,for us to connect to.
 
Problem with this requirement, is the ambiguity.
What are “similar switchgear assemblies”?
My understanding is that it is intended to encompass TPN DBs when used in a domestic setting. Why they didn't just state "distribution boards" instead of "consumer units and similar switchgear assemblies" is a mystery though.
 
From what I gather, all the old group of standards (BS EN 60439-1 to 4) that related to low voltage switchgear, have been changed to BS EN 61439-1 to 4.
BS EN 61439-1 covers type-tested assemblies or Consumer Units.
BS EN 61439-2 covers partially type-tested assemblies. (Whatever one of those is?)
BS EN 61439-3 covers type tested assemblies intended to be used by unskilled or ordinary persons.
New name DBO (Distribution Boards intended for use by Ordinary persons). i.e. a TP&N DB used in a domestic setting (as long as it has been type tested).
 
We had RECs for about 10 years, from when the CEGB was privatised to when they allowed anyone to sell you electricity.
The RECS would distribute and supply electricity, now the DNOs distribute and others (such as British Gas, Sainsbury’s, Zog, etc.) supply.
 
I typically flatten the tails with pliers, tighten them, wiggle, retighten and then periodically check them as I work on the board.

I find that deliberately untwisting the strands helps a lot to get the termination snug. The strands can then move freely as the terminal is tightened, so reducing the possibility of strands moving later.

ESF investigation on termination of meter tails:

Tightness of Meter Tails - https://www.----------------------------/electrical-professionals/product-safety-unit/tightness-of-meter-tails/
 
ESF investigation on termination of meter tails:

Tightness of Meter Tails - https://www.----------------------------/electrical-professionals/product-safety-unit/tightness-of-meter-tails/

That's all well and good but they seem to have missed the point about checking to see if said isolators in fuseboards are not fit for purpose......

Those old wylex units with 2 screws on the incoming tails never seem to self ignite!
 

Reply to Main isolation by local REC in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
372
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
937
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
https://www.edwardes.co.uk/products/mk-k1257whi-logic-plus-1gang-13amp-non-standard-dp-switch-socket?gad_source=1&gclid=EAIaIQobChMI7POp_pHFhgMVk5J...
Replies
1
Views
355
  • Question
Yes like that - fitted last week 😂
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top