I have been asked to bond the gas and water of my neighbours house as British Gas have picked it up as not bonded.

The consumer unit is an old Wylex one with re-wireable fuses. Ideally needs replacing with MCBs and RCD protection but they are not willing to do that until next year.

As the house is an "upside down" house, the stopcock for the water is upstairs in the kitchen which is a nightmare. The regs say that it needs to be bonded 600mm of entry or "where practical." If I can locate the water pipe downstairs, would this be acceptable or does it need to be on the consumers side of the stop cock?

The gas meter is outside in a box, so again, can I just find the closest point of entry to the house which is practical to bond?

Is supplementary bonding to sink, boiler etc required as it's an old consumer unit?

Is bonding notifiable or need to be signed off?

Thanks in advance
 
Last edited by a moderator:
It is what it is ... connect at closest point of entry, BUT first does it need to be bonded??

Don't get involved in trying to shove wires into the meter box. It's not necessary

If BG had their way we would be bonding the towel rail and the door handles.

Test it first to see if it needs bonding.

Notifiable? ... signed off ????? What's that all about?? ;)
 
The consumer unit is an old Wylex one with re-wireable fuses. Ideally needs replacing with MCBs and RCD protection but they are not willing to do that until next year.
Irrelevant and not really true.

The regs say that it needs to be bonded 600mm of entry or "where practical."
The 600mm. only applies to meters indoors where they are at the point of entry.

If I can locate the water pipe downstairs, would this be acceptable or does it need to be on the consumers side of the stop cock?
Is the point of entry there?

The gas meter is outside in a box, so again, can I just find the closest point of entry to the house which is practical to bond?
Yes.

Is supplementary bonding to sink, boiler etc required
Not unless they are in a special location.

as it's an old consumer unit?
Nothing to do with the CU which you seem to dislike.

Is bonding notifiable or need to be signed off?
No.
 
Thanks very much for the replies, great help.

I thought supplementary bonding was required if disconnection times weren't met? I haven't tested the consumer unit yet but would that be basing it on the disconnection time of the whole consumer unit?
 
Plumbers and the likes = pains in the arse. I did a cu swap last week on a TNS System it was already bonded in 6 mm but not where it should be so I verified via test and got a reading of 0.02, 0.05 been the lowest acceptable. I even put labels where the earth clamps should be stating the fact! Two days later customer calles me in a panic! Plumber been round and issued her with a piece of paper saying DANGER DANGER WARNING WARNING all over it in big red letters. Dikc heads!
 
Plumbers and the likes = pains in the arse. I did a cu swap last week on a TNS System it was already bonded in 6 mm but not where it should be so I verified via test and got a reading of 0.02, 0.05 been the lowest acceptable. I even put labels where the earth clamps should be stating the fact! Two days later customer calles me in a panic! Plumber been round and issued her with a piece of paper saying DANGER DANGER WARNING WARNING all over it in big red letters. Dikc heads!

What did the piece of paper say?
 
If he was anything like the plumbers at my company, he wouldn't look out of place at remploy.

plumbers work to different rules to us sparks just as our supply companies work to different rules to us (ie. insisting on 25mm tails when they install only 16mm) a bit of continuity wouldn't go a miss. I still come across plumbers who ask for cross bonding on boilers etc. bonding is our job leave us to it.
 
They do indeed have their little eccentricity foibles...i have a plumber friend "i'm NOT a plumber,i'm a heating engineer"....yawn... who insists i come and bond his five copper runs under the boiler,all pretty and without joints,whether or not it needs it because "i ALWAYS do it this way..." He likes them on show and always points this out to his customer even if they look bored. I really think if he could,he would illuminate this bonding with a LED uplighter and have Dido playing in the background...
 
But, surely they will be.

Are you getting confused with ONE of the conditions for the omission of supplementary bonding IN special locations when all of the circuits have RCD protection?
701.415.2

So basically, supplementary bonding isn't required if final circuits (assuming this doesn't include lights) in special locations have RCD protection?

Therefore, if the special location doesn't have a final circuit, then supplementary bonding isn't required at all?
 
They do indeed have their little eccentricity foibles...i have a plumber friend "i'm NOT a plumber,i'm a heating engineer"....yawn... who insists i come and bond his five copper runs under the boiler,all pretty and without joints,whether or not it needs it because "i ALWAYS do it this way..." He likes them on show and always points this out to his customer even if they look bored. I really think if he could,he would illuminate this bonding with a LED uplighter and have Dido playing in the background...

You think you have problems ... what about me?

When I was working, I was qualified to work in both camps, so when I was fitting boilers I bonded all the pipes at the boiler, but when I was sparking I didn't.

Talk about being schizoid!!
 
So basically, supplementary bonding isn't required if final circuits (assuming this doesn't include lights) in special locations have RCD protection?

Therefore, if the special location doesn't have a final circuit, then supplementary bonding isn't required at all?
Lighting is a final circuit as well.
If there is no electricity used in the special location then supplementary bonding is not required.
If all the low voltage circuits in the special location are protected by ADS and all main bonding is in place and there is a 30mA RCD protection to all of these circuits, then, supplementary bonding is not required.


For all locations if, because of a particular difficulty with a circuit, it is not possible to meet the required disconnection times for ADS then supplementary bonding may be needed to ensure the safety of the installation, however this would only be for a few specialised situations.
 

Reply to Main Protective Bonding - Gas and Water in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
327
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
303
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
365

Similar threads

I like your way of thinking.
Replies
6
Views
588
loz2754
L
Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
642
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top