I believe the reading of 0.05 ohms is to do with the pipe work going live under fault conditions and bringing all extranias conductive parts to no more than 50 volts touch voltage !!
 
Last edited:
The 0.05Ω figure comes from guidance note 3, but i am led to believe its use is set to become clearer in the present reviews of BS7671 etc that are about to be published. When me and Chr!s have asked questions of the IET about it they have been decidedly vague.
 
Not looking for an arguement but how does 131.8 say that its ok to leave as is? As I read it it says you can't make additions or alterations unless the existing is adequate. I had a discussion with my assessor and he said that 6mm bonds were ok if they showed no signs of deterioration but the PME regs require 10mm. Where do you get the 0.05ohms figure from?

I got the advice from Elecsa (who reminded me where to find it in GN3)
 

Reply to Main protective bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
840

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
487

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top