Discuss main RCD trips before RCD 30ma spur in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
sorry it is a power shower! so cable is fine
ive got a feeling someone put that in to stop it tripping out the house, (because it kept tripping) but who knows, ill give it ago
sorry it is a power shower! so cable is fine
correct ,they should both trip as the first rcd in line allows enough fault current to pass to trip the second one ,however the first should trip too,Are you saying that you have a 1.5mm cable feeding an 8.5KW shower?? or have i miss read your post??
As for the 30mA RCD spur unit, ...if the main RCD is also 30mA then your lucky they both don't trip together, as there is no discrimination between them!!!