Main Switch twitch...... | on ElectriciansForums
Guest viewing is limited
Discuss Main Switch twitch...... in the UK Electrical Forum area at ElectriciansForums.net
Is there any good reason why you shouldn't use an rcd as a main switch in a domestic installation thats tns/ tncs ?
To me there are two separate questions here:
  • Can a RCD act as the main isolation switch?
  • Is it acceptable to have one RCD for 30mA "additional protection" of all circuits?
For the 1st point, then yes the usual double-pole RCD can be a main switch providing it is rated to at least the maximum system current. So on a 60A fuse the RCD should be 63A or more, etc. Sometimes you will find the sum of MCBs is lower than the supply fuse, so that is another means for limiting total load to the RCD's rating.
For the 2nd point then I would say no, it is poor practice as everything goes off on any trip and as that includes all lights, a safety risk as well. Additionally the accumulated leakage of a whole installation makes spurious trips far more likely to happen.
TL;DR Fine for a 100mA or 300mA delay incomer (as used for TT or farm/fire risk, even if supply is TN) where you have separate groups of 30mA protection, poor for general use except for a very small installation.
nice one
In this case, I guess you should use a type A rcd or type F , rather than the more common type AC.
Realistically type AC ought not to be made any more (or even for last few years) as so many products have some capacity to leak an element of DC.
As @ImpededLoop says most RCBO (at least all I have seen in recent years) are type A which ought to be your base line for RCD/RCBO choices.
There are excellent answers above which I agree with.
It's quite common (in my area at least) to find a semi-rural row of 2 up 2 down terraces with overhead supply, TT earthing, and a fairly old 5 way consumer unit with an RCD main switch.
My additional comment would be that the chances of pressing the test button are (even) lower than the usual 0% if you lose all power at once by doing so, and RCD's need occasional exercise to continue doing the job they are designed to do. To my thinking there is an increased risk of the RCD not working when it's the main switch as it's probably sat there untested most of it's life.
Agreed! If never tested you have no idea if it would detect a fault and even if it does, would the mechanism actually trip OK.
If I were installing a CU for a TT system it would be a 100mA delay RCD as incomer and RCBOs for the individual circuits. Sure the 30mA protection might have failed so you don't have proper shock protection, but a 100mA delay is better than nothing and it prevents the CPC/earth rod sitting at 230V as would otherwise happen if the only RCD failed to trip So whole-house ADS is far better than none at all!
Reply to Main Switch twitch...... in the UK Electrical Forum area at ElectriciansForums.net
Obviously you need to check the means of earthing, Ze, and polarity no matter what for the EIC. As above, if anything looks dodgy then EICR is a...
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...