we are moving for 2 years and i want to rent my house. electrician failed my house eicr for not having waterpipe earth bond. i belive it has one but the pipe is plastered in except for the stopcock so its not visible. i think he tried to take the p.. becaue he seemed surprised when i asked him what the resistance was, first he said no earth wire in breaker box, and was fishing for work running a new wire to stopcock, but when i enquired more he got a bit nervous, said he wanted to doble check the box znd lo and behold he found one. it measures zero ohms beteeen this wire and waterpipe close by but obviously cant see if it bonded close to stopcock due ton1940s house and pipe being boxed plasterd in.
so basically, should it have failed?

thanks in advance
 
The continuity and resistance between the pipe and the end of the bonding cable at the consumer unit needs verifying. Zero ohms? Not really possible...obviously the lower the better but zero ohms...hmmm. The earth clamp on the pipe should also be visible and accessible, but may not be on an older install.
 
check the size of the earth cable, if its old it may be too small in csa
it should be 10mm
try chopping out the plaster around the stop cock to expose the clamp(it must be fitted on the outgoing side of the cock )
btw-if thats all he could find wrong he sounds like a good fella
 
check the size of the earth cable, if its old it may be too small in csa
it should be 10mm
try chopping out the plaster around the stop cock to expose the clamp(it must be fitted on the outgoing side of the cock )
btw-if thats all he could find wrong he sounds like a good fella

The cable is visible in the CU so easy to check csa ;)

EDIT: posted before finishing.......
I agree with Tel, C3 if it measures out ok.
 
A simple test from stop cock to CU wandering lead would check for any good old ohms, if the cable size was ok at board, also agree remove plaster to expose clamp, you should be able to see this for good practice anyway. good luck.
 

Reply to main waterpipe sealed up should it fail e.i.c.r. ? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
372
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top