Guys, need some advice.

When measuring across some cctv cables, im getting around 0.80 v of AC, which in turn is causing mass problems with the system.

I have seen in our basement that the lv cables are run less than 2 inches away from the mains cables, so im sure the magnetic field is inducing the lv cables.

question being would a rubber mat between the 2 cables stop the magnetic field or is there another solution???

The run is around 20m in length

Any help would be greatly appreciated

Tom
 
Can't see how a rubber mat would stop induction. Also, 2" sounds a fair gap between the two I would have thought. The 0.8V could be normal - is it composite video we're talking on the cctv cables? Daz
 
Thanks for your input guys. Our sub - contractors who i wont name have quoted a hell of a lot of money to sort the problem with the cctv. We feel theyre trying to pull a fast one.

Be nice to get to the bottom of it without this cost.

Thanks again.
 
If there's at least an inch separation distance along a 20m run I doubt it's induced voltages causing your problems. Is the video cable a shielded type? Is the shield connected either to a ground or a designated shield termination point? Can you give more info about the type of equipment and the type of cabling?
 
Last edited:
Good mention of the sensitivity of digital gear.This can be demonstrated to apprentices by showing an AC or DC voltage across a wet hair...
 
Works even better with your head jammed in a busbar chamber :)

On a serious note (and risking being shot out of the water), isn't the rule that you can have band 1 and 2 cables in the same trunking as long as they are seperated by a plastic wall? This would bring them a lot closer than the recommended 50mm seperation. I can't see what difference a 2mm strip of plastic (or a rubber mat) is going to make to an induced current, or am I missing something?
 

Reply to mains cables inducing LV cables in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top