Guys, need some advice.

When measuring across some cctv cables, im getting around 0.80 v of AC, which in turn is causing mass problems with the system.

I have seen in our basement that the lv cables are run less than 2 inches away from the mains cables, so im sure the magnetic field is inducing the lv cables.

question being would a rubber mat between the 2 cables stop the magnetic field or is there another solution???

The run is around 20m in length

Any help would be greatly appreciated

Tom
 
Can't see how a rubber mat would stop induction. Also, 2" sounds a fair gap between the two I would have thought. The 0.8V could be normal - is it composite video we're talking on the cctv cables? Daz
 
also bear in mind that a digital meter will show this sort of voltage with nothing there, if you are within 5 miles of 230V.
 
Thanks for your input guys. Our sub - contractors who i wont name have quoted a hell of a lot of money to sort the problem with the cctv. We feel theyre trying to pull a fast one.

Be nice to get to the bottom of it without this cost.

Thanks again.
 
If there's at least an inch separation distance along a 20m run I doubt it's induced voltages causing your problems. Is the video cable a shielded type? Is the shield connected either to a ground or a designated shield termination point? Can you give more info about the type of equipment and the type of cabling?
 
Last edited by a moderator:
Works even better with your head jammed in a busbar chamber :)

On a serious note (and risking being shot out of the water), isn't the rule that you can have band 1 and 2 cables in the same trunking as long as they are seperated by a plastic wall? This would bring them a lot closer than the recommended 50mm seperation. I can't see what difference a 2mm strip of plastic (or a rubber mat) is going to make to an induced current, or am I missing something?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
mains cables inducing LV cables
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
tuckerkop81,
Last reply from
Stroppy,
Replies
10
Views
2,251

Advert

Back
Top